Hi Guys,
I'm trying to configure the Analog outputs (AO1,AO2) of TM172E28R expansion module to 4-20mA output (current modulation) but having problems with it.
I've configure both AO1 and AO2 as value '0' (current modulation) under Advanced Settings.
And then I do the full download. Everything complies fine with no error but when I test the outputs with a multimeter both outputs are showing around 40-50mA no matter what the programming value being 0-1000.
If I measure the AO3 and AO4 of the main controller, it correctly shows value within 4-20mA.
What am I doing wrong here?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-24 02:57 AM
Hi,
Have you done a download all and reboot of the PLC?
Configuration is sent to expansions during the PLC boot phase.
If you have a TM171ADMI, you can disconnect the CAN bus and connect directly to the expansion using ESME HVAC Installer and TM171ADMI. Once connected you can verify the I/O settings and manually test them.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-24 02:57 AM
Hi,
Have you done a download all and reboot of the PLC?
Configuration is sent to expansions during the PLC boot phase.
If you have a TM171ADMI, you can disconnect the CAN bus and connect directly to the expansion using ESME HVAC Installer and TM171ADMI. Once connected you can verify the I/O settings and manually test them.