Hello,
I have a TM172PBG18R, and I'm trying to configure the Ethernet to use BACnet IP. However, I couldn't find the option under Configuration > M172 07-18 I/Os > Ethernet.
The manual mentions that this feature is disabled by default, so I’d like to know how to enable it. Also, would I need some sort of BACnet library to program it in Ecostruxure Machine Expert HVAC?
I'm new to PLC development, so I apologize if this is a basic question.
Thank you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-07 10:20 PM
Hi, This is the value you are looking for
You have to set the value to 0 to activate the BACnet IP Port
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-07 10:20 PM
Hi, This is the value you are looking for
You have to set the value to 0 to activate the BACnet IP Port