Posted: 2023-04-06 04:06 AM
Is there an alternative way to program a TM171 besides the TM171ADMI or the TM171AMFK ? Both products are unavailable (discontinued) locally and I need to program some PLCs.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-06 04:16 AM
You could download also with any RS485 adapter the project. But only in the case you have the Modbus version. Alternative to this way you could use the new communication Modul for TM171O TM171ALAN
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-06 04:16 AM
You could download also with any RS485 adapter the project. But only in the case you have the Modbus version. Alternative to this way you could use the new communication Modul for TM171O TM171ALAN