TM171 Alarms
HVAC and Pumping Forum
Select a Country
  • Industrial Automation
  • HVAC and Pumping Forum
  • TM171 Alarms
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
otrotabi
otrotabi
Contributor
Posted: ‎2022-06-29 11:18 AM
1803
TM171 Alarms
I know thta defining variables (which are assigned USINT values by defaut)  under the "Alarms" folder acivates the Alarm icon on the top left of the display if the variable is set to 1, for example AL00 := 1; will turn the alarm icon ON and will show "PMOT" on the AL menu accesible with the SET button.
I´ve also discovered by chance that if you do: AL00 :=2; the alarm icon will blink instead.
So I load these variables memory addresses to an array with a task at Init like this : Alarm[0].MemAddress := ?AL00; and then  for example "Alarm[6].@MemAddress := TO_USINT(CompressorAlarmId.b0)"; will turn the compressor motor alarm ON if the output bit from compressor alarm management turns to ON.
My question is: is there anyway to access "Short Names" programmatically as well ? Can they be changed on the fly without re-programming the PLC ?
  • HVAC
  • HVAC.English
  • TM171
FedericoM
FedericoM Mentor
Mentor
Posted: ‎2022-06-30 11:51 PM
1758
the scope of Alarm folder defined in the M171O projects is to automatically create a dynamic Alarm menu (Set-->AL) on the M171O local display.
Alarm folder is present on other project targets just for porting reason.
Basically if an alarm variable has value 1 (assumed as active alarm) or 2 (assumed as alarm which can be reset), the related short name will be visible in the AL folder, if it is 0 it will be hidden.
The Alarm icon is on if at least an alarm variable has value 1.
The Alarm icon blink if at least an alarm variable has value 2 and all other have value 0.
Short name can't be changed runtime.
  • Ecostruxure machine expert HVAC
FedericoM
FedericoM Mentor
Mentor
1759
otrotabi
otrotabi
Contributor
Posted: ‎2022-07-01 03:48 AM
In response to FedericoM
1748
Thank you.
May the short name be read sowehow (other than physically reading it on the Set/Al menu I mean) ? I am using an alarm system which makes use of the "OverwriteLocalDisplay" Function to automatically display the alarm on the screen as it happens, it would be nice if I did not have to two tables synced manually.
FedericoM
FedericoM Mentor
Mentor
Posted: ‎2022-07-01 04:23 AM
In response to otrotabi
Unfortunately it is not possible...