Problems using TM3DM8R-module TM3 - 8 IO relays

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • Problems using TM3DM8R-module TM3 - 8 IO relays
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Commander FedericoM Commander
74
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
50
LeTomas
Lt. Commander LeTomas Lt. Commander
14
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Solved
Anonymous user
Not applicable

Posted: ‎2020-02-11 06:53 AM . Last Modified: ‎2020-09-10 12:53 AM

1 Like
6
3302
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-11 06:53 AM . Last Modified: ‎2020-09-10 12:53 AM

Problems using TM3DM8R-module TM3 - 8 IO relays

Hi community, I have trouble using this product, because the green LED does not indicate

when I connect one input end and its common to 24Vdc and the corresponding output does have

the so called relay output when checking continuity.

 

Thank you for input in advance.

 

 

 

 

Link to the product TM3DM8R page: https://www.se.com/hk/en/product/TM3DM8R/module-tm3---8-io-relays/

Labels
  • Labels:
  • Modicon M2xx
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-02-11 01:12 PM . Last Modified: ‎2020-02-11 07:59 PM

1 Like
4
3291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-11 01:12 PM . Last Modified: ‎2020-02-11 07:59 PM

To confirm, you have your wiring as indicated in the diagrams below, with the -ve terminal of the 24VDC power supply wired to the COM0 terminal, the +ve of the 24VDC power supply providing voltage to your 'sensor' and then the sensor output wired to the input terminal (I0 through I3)?

 

If you bypass the sensor, and directly wire the +ve terminal from the 24VDC power supply to I0 does an LED illuminate then?

 

I assume that you do have the TM3DM8R installed within a rack, with a 'receiver'/'controller' in that rack supplying the 5V operating voltage for the IO card itself.

 

And when you drive the Q0 through Q3 outputs from your PLC, does the LED for the associated output turn on?

 

2020-02-12 08_08_08-Modicon TM3 - Digital I_O Modules - Hardware Guide.png


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Omaelk
Janeway Omaelk
Janeway

Posted: ‎2020-02-11 07:43 AM

0 Likes
0
3298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-11 07:43 AM

Hey @Anonymous user  , thank you for your question
 
I moved it to this forum where the community of experts will be able to provide you the right support and solve your issue! 
 
PS: don't hesitate to check the Knowledge base and use the search bar with keywords. there is a lot of content discussed everyday and your issue may have already been solved 😉

 

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-02-11 01:12 PM . Last Modified: ‎2020-02-11 07:59 PM

1 Like
4
3292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-11 01:12 PM . Last Modified: ‎2020-02-11 07:59 PM

To confirm, you have your wiring as indicated in the diagrams below, with the -ve terminal of the 24VDC power supply wired to the COM0 terminal, the +ve of the 24VDC power supply providing voltage to your 'sensor' and then the sensor output wired to the input terminal (I0 through I3)?

 

If you bypass the sensor, and directly wire the +ve terminal from the 24VDC power supply to I0 does an LED illuminate then?

 

I assume that you do have the TM3DM8R installed within a rack, with a 'receiver'/'controller' in that rack supplying the 5V operating voltage for the IO card itself.

 

And when you drive the Q0 through Q3 outputs from your PLC, does the LED for the associated output turn on?

 

2020-02-12 08_08_08-Modicon TM3 - Digital I_O Modules - Hardware Guide.png


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-02-11 06:28 PM . Last Modified: ‎2020-02-11 06:32 PM

In response to BevanWeiss
1 Like
3
3287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-11 06:28 PM . Last Modified: ‎2020-02-11 06:32 PM

Sorry, I don't know what sensor is, the wiring diagram just shows as a switch to me.

Also what's the 5V rack? There's no mention about that in this datasheet: https://docs.rs-online.com/8a48/0900766b8150cd45.pdf

 

Do you mean that white socket for the 5V power supply? I thought it's for expansion module?

InkedCapture_LI.jpg

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-02-11 06:35 PM

In response to Anonymous user
0 Likes
2
3275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-11 06:35 PM

There is definitely a mention of the 5V rack / bus connection in the datasheet.

 

2020-02-12 13_29_29-0900766b8150cd45.pdf.png

The IO module simply will not work unless it is installed within a rack, and at this stage you haven't provided any indication that you have indeed installed it within a rack, nor that you have a PLC to control this IO module.

 

Please provide photo(s) that show your current installation, including the 24VDC Power Supply, the connections to your processor/PLC, the connections to your TM3DM8R IO Module, and the connections to your 'switch' or sensor.

 

These photos should be clear enough to identify EXACTLY which terminals the connections are made to, and EXACTLY which part numbers are in use for the PLC/IO Module.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-02-11 06:56 PM

In response to BevanWeiss
0 Likes
1
3271
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-11 06:56 PM

So is it connected via bus connector to the white socket?

Currently, I haven't installed in rack nor have PLC control yet.

Thank you for your replies, I guesss I understand what I am missing.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-02-11 07:08 PM

In response to Anonymous user
1 Like
0
3269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-11 07:08 PM

That plug is indeed what is supposed to connect this IO Module into the 'bus' of the other IO Modules / CPU.

The CPU is what is responsible for reading the inputs from this module, and driving the bits for the outputs.

 

The module itself (without a CPU to control it) is quite useless.

 

Once you have the CPU etc configured if you have another problem, please raise this as a separate topic here.

And given it sounds like at least one of my responses has 'solved' your problem, please mark one as the solution here.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of