Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Multiple functions in Application_Addons Library (v1.3) are written for case insensitive environment

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • Multiple functions in Application_Addons Library (v1.3) are written for case insensitive environment
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
EcoStruxure™ Machine Expert - HVAC

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
obscuresc
obscuresc
Troubleshooter

Posted: ‎2020-09-16 07:38 PM . Last Modified: ‎2020-10-07 03:15 AM

0 Likes
8
5983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-16 07:38 PM . Last Modified: ‎2020-10-07 03:15 AM

Multiple functions in Application_Addons Library (v1.3) are written for case insensitive environment

Hi all,

 

I'm using the latest version (v1.3) of the Application_Addons Library that is available in 'Toolbox SE M17x' via Box.

Some of the functions are written with lower case syntax and a majority also neglect using semi-colons on 'THEN's.

 

While the lack of semi-colons do not cause compile-time errors in my environment, the lower case syntax does.

I've been maintaining consistent case so far and have the case sensitive option enabled in 'Project options->Code generation'.

 

Could this library be updated with this in mind?

 

Cheers,

Jack

 

 

 

 

 

Labels
  • Labels:
  • HVAC
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-10-07 02:37 AM . Last Modified: ‎2020-10-07 03:09 AM

0 Likes
0
5898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-07 02:37 AM . Last Modified: ‎2020-10-07 03:09 AM

Hi Jack,

 

thanks for your feedback. We will take this into account for the next release.

 

@FedericoM FYI

 

Best regards,

Pierpaolo

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Rodrigo_Garcia
Rodrigo_Garcia Mentor
Mentor

Posted: ‎2020-09-24 02:39 AM

0 Likes
1
5950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-24 02:39 AM

Hello François, @Anonymous user : Could you please help?

 

Regards.

Rodrigo G. 


Industrial Automation Community manager

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-09-24 02:43 AM

In response to Rodrigo_Garcia
0 Likes
0
5947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-24 02:43 AM

@Anonymous user,: Hello Pierpaolo, can you ave a look at this request ? Thank you

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-10-07 02:37 AM . Last Modified: ‎2020-10-07 03:09 AM

0 Likes
0
5899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-07 02:37 AM . Last Modified: ‎2020-10-07 03:09 AM

Hi Jack,

 

thanks for your feedback. We will take this into account for the next release.

 

@FedericoM FYI

 

Best regards,

Pierpaolo

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
FedericoM Mentor
Mentor

Posted: ‎2020-10-09 03:37 AM . Last Modified: ‎2020-10-09 03:41 AM

0 Likes
4
5859
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-09 03:37 AM . Last Modified: ‎2020-10-09 03:41 AM

Hello Jack,

 

I've uploaded an updated version 1.3.1 on box.

Please let me know if it solved your issues.

 

Federico

 

@obscuresc @Anonymous user 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

obscuresc
obscuresc
Troubleshooter

Posted: ‎2020-10-11 03:24 PM

In response to FedericoM
0 Likes
0
5844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-11 03:24 PM

Hi @FedericoM,

 

Didn't quite solve my issues; the functions in the BU2SI folder the ones I have issue with.

 

Cheers,

Jack

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

KCWong
KCWong Troubleshooter
Troubleshooter

Posted: ‎2020-10-14 09:06 PM

In response to FedericoM
0 Likes
2
5801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-14 09:06 PM

Please send me the Box link. Thanks.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

obscuresc
obscuresc
Troubleshooter

Posted: ‎2020-10-14 09:12 PM

In response to KCWong
0 Likes
1
5799
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-14 09:12 PM

 

https://schneider-electric.app.box.com/s/3lc7iz6mjnfir5nj75l9kb6vbueqfkui/folder/50956872239

 

Jack

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

KCWong
KCWong Troubleshooter
Troubleshooter

Posted: ‎2020-10-14 09:14 PM

In response to obscuresc
0 Likes
0
5797
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-14 09:14 PM

Thanks a lot.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore