Modicon M172 analog output

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • Modicon M172 analog output
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Commander FedericoM Commander
68
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
47
LeTomas
Lt. Commander LeTomas Lt. Commander
14
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to HVAC and Pumping Forum
pawel_kowalski_
Commander pawel_kowalski_
Commander

Posted: ‎2020-12-11 01:29 AM

0 Likes
3
2926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-11 01:29 AM

Modicon M172 analog output

Hi All,

 

I have problem with analog outputs AOL1-AOL4 the outputs AOL3 and AOL4 I configure in program as voltage modulation.
I want using this outputs to control device like valve with input 0-10V. I wrote program I see the output is on working but when I measuring output physically using a multimeter there wasn't be a voltage.

Even I wrote a test program to check all analog outputs and when I measuring every output I saw that on analog output AOL5 the voltage was changing propertly.
Where can ba a problem?
I using Machine Expert - HVAC 1.2.1 and modicon 172 File version 596.10

 

Labels
  • Labels:
  • HVAC
  • Tags:
  • analog output
  • english
  • hvac
  • M172
  • Machine Expert
  • problem
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Ismet_S
Ensign Ismet_S Ensign
Ensign

Posted: ‎2020-12-11 06:08 AM

1 Like
0
2916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-11 06:08 AM

Hi Pawel,

 

Please check page 99 of attached Hardware Guide M172P Hardware Guide

 

Only AO3 and AO4 are “configurable” output, and the remaining are set, by defaultm as low voltage analog output 0..10v.

It could be, that the Bios parameter Cfg_Aox has not been configured properly for those two Analog output.

This can be checked directly under the “Commissioning” Tab from the application when connected to the hardware. And the value read should be “2” for Voltage modulation.

Also, make sure that your load resistance is more than 700Ohm

Hope this helps.

Feel free to back to us if you have any questions.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2021-01-14 02:06 AM

1 Like
0
2820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-14 02:06 AM

If you define AO3 and 4 as voltage output via BIOS Parameter through configuration you have to do a download all.download all.PNG

If you download only Programming the default values for Bios and EEPROM would not be written.

app.PNG

Alternativ you can write AO3 and 4 to 0..10V directly via Commissioning or via Webserver 10.0.0.100*/evoindex.htm

(* replace with IP of controller) 

web.PNG

ao.PNG

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

SalahZahra
SalahZahra
Cadet

Posted: ‎2024-10-08 05:45 AM

0 Likes
0
609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-08 05:45 AM

in program , you have to multiply output value by 100
so, to get 10 VDC , you have to write to assigned output vibrable 1000

and so on 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of