Modbus RTU communication issue between TM172OBM18R and Weintek MT6051iP over RS-485
HVAC and Pumping Forum
Select a Country
  • Industrial Automation
  • HVAC and Pumping Forum
  • Modbus RTU communication issue between TM172OBM18R and Weintek MT6051iP over RS-485
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
Lautaro25-02-98
Lautaro25-02-98
Explorer
Posted: ‎2025-11-28 04:25 AM
574
Hi everyone,
I’m trying to communicate a TM172OBM18R PLC with a Weintek MT6051iP HMI using Modbus RTU over RS-485, but I always get a communication error on the HMI.
Hardware / software
- PLC: TM172OBM18R
- Software: EcoStruxure Machine Expert – HVAC
- HMI: Weintek MT6051iP
- Software: EasyBuilder Pro
- Link: RS-485 1-wire (D+ / D– with common GND)
PLC configuration (Machine Expert – HVAC)
Using RS485-1 On Board:
- Proto_RS485_1 = 3 – Modbus RTU
- Baud_RS485_1= 38400
- DataBit_RS485_1 = 8
- StopBit_RS485_1 = 1
- Parity_RS485_1 = Even
- Addr_RS485_1 = 1 (slave ID)
In Configuration → Modbus objects I created some Modbus objects mapped to %MWx words and assigned them to interface RS485-1 so they can be accessed by an external Modbus master.
The PLC program compiles and runs fine.
HMI configuration (EasyBuilder Pro)
- Device: tested both “MODBUS RTU (Adjustable)” and “Schneider MODBUS RTU”
- COM Port: COM1 – RS485 1-wire (physical port wired to the PLC)
- Baudrate: 38400
- Data bits: 8
- Parity: Even
- Stop bits: 1
- Station No.: 1 (same as PLC)
I’m trying to read one simple word (for example %MW0 mapped in the Modbus objects table) using the corresponding Modbus address in the HMI tag.
Wiring
- PLC D+ → HMI Data+
- PLC D– → HMI Data–
- PLC GND → HMI GND/COM
Polarity and continuity were checked; there are no wiring faults.
Symptom
The HMI always indicates a communication timeout with the PLC: the device status shows a communication error and no valid data is received from the PLC, even though baudrate, parity, ID, etc. match on both sides.
What I’ve already tried
- Switched between RS485-1 On Board and RS485-2 On Board (updating the Modbus objects interface accordingly).
- Tried different baudrates and parity settings.
- Tested both HMI drivers (generic Modbus RTU and Schneider Modbus RTU).
- Rechecked cabling and commissioning parameters multiple times.
Questions
1. For this kind of external HMI connection, what is the recommended interface on the TM172: the RS485 on-board ports or the RS485 plugin passive interface?
2. Are there any official examples or application notes showing Modbus RTU communication between M171/M172 controllers and third-party HMIs?
Any help or hints would be greatly appreciated.
Best regards,
Lautaro Tapia
  • HVAC
ismailozinan
ismailozinan Leader
Leader
Posted: ‎2025-11-30 04:40 AM
Is it possible check cabling and TM172 modbus settings? Please make sure that the TM172 RS-485 settings are correctly configured as attached.
BR.
ismailozinan
ismailozinan Leader
Leader
BR.