Modbus RTU communication issue between TM172OBM18R and Weintek MT6051iP over RS-485

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • Modbus RTU communication issue between TM172OBM18R and Weintek MT6051iP over RS-485
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Captain FedericoM Captain
96
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
56
M_Cervati
M_Cervati Support
17
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to HVAC and Pumping Forum
Start a Topic
Lautaro25-02-98
Lautaro25-02-98
Cadet

Posted: ‎2025-11-28 04:25 AM

0 Likes
1
127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-28 04:25 AM

Modbus RTU communication issue between TM172OBM18R and Weintek MT6051iP over RS-485

Hi everyone,

I’m trying to communicate a TM172OBM18R PLC with a Weintek MT6051iP HMI using Modbus RTU over RS-485, but I always get a communication error on the HMI.

Hardware / software

- PLC: TM172OBM18R
- Software: EcoStruxure Machine Expert – HVAC
- HMI: Weintek MT6051iP
- Software: EasyBuilder Pro
- Link: RS-485 1-wire (D+ / D– with common GND)

PLC configuration (Machine Expert – HVAC)

Using RS485-1 On Board:

- Proto_RS485_1 = 3 – Modbus RTU
- Baud_RS485_1= 38400
- DataBit_RS485_1 = 8
- StopBit_RS485_1 = 1
- Parity_RS485_1 = Even
- Addr_RS485_1 = 1 (slave ID)

In Configuration → Modbus objects I created some Modbus objects mapped to %MWx words and assigned them to interface RS485-1 so they can be accessed by an external Modbus master.

The PLC program compiles and runs fine.

HMI configuration (EasyBuilder Pro)

- Device: tested both “MODBUS RTU (Adjustable)” and “Schneider MODBUS RTU”
- COM Port: COM1 – RS485 1-wire (physical port wired to the PLC)
- Baudrate: 38400
- Data bits: 8
- Parity: Even
- Stop bits: 1
- Station No.: 1 (same as PLC)

I’m trying to read one simple word (for example %MW0 mapped in the Modbus objects table) using the corresponding Modbus address in the HMI tag.

Wiring

- PLC D+ → HMI Data+
- PLC D– → HMI Data–
- PLC GND → HMI GND/COM

Polarity and continuity were checked; there are no wiring faults.

Symptom

The HMI always indicates a communication timeout with the PLC: the device status shows a communication error and no valid data is received from the PLC, even though baudrate, parity, ID, etc. match on both sides.

What I’ve already tried

- Switched between RS485-1 On Board and RS485-2 On Board (updating the Modbus objects interface accordingly).
- Tried different baudrates and parity settings.
- Tested both HMI drivers (generic Modbus RTU and Schneider Modbus RTU).
- Rechecked cabling and commissioning parameters multiple times.

Questions

1. For this kind of external HMI connection, what is the recommended interface on the TM172: the RS485 on-board ports or the RS485 plugin passive interface?

2. Are there any official examples or application notes showing Modbus RTU communication between M171/M172 controllers and third-party HMIs?

Any help or hints would be greatly appreciated.

Best regards,
Lautaro Tapia

Labels
  • Labels:
  • HVAC
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
ismailozinan
Commander ismailozinan Commander
Commander

Posted: ‎2025-11-30 04:40 AM

0 Likes
0
97
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-30 04:40 AM

Hi,

Is it possible check cabling and TM172 modbus settings? Please make sure that the TM172 RS-485 settings are correctly configured as attached.

BR.

 

 

Bit.jpgPLC.jpgPLCCable.jpgSystem.jpgWord.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore