Hi,
I am setting up BACnet on TM172PDG18R. I have created a device object with the following properties
After downloading the project, and connecting via Yabe, the device appears correctly.
If I attempt to change the Object Name of the Device Object, I receive an 'ERROR_CODE_WRITE_ACCESS_DENIED'.
Document EIO0000004776 06/2022 'BACnet Application Notes' indicates that this property is writable.
If I go into the Configuration pane of ESME HVAC, I can edit the register associated, and the object name in Yabe will change.
Does mean that the object name is only available for edit via Modbus or via programming on the IEC-side?
Thanks,
Jack
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-05 01:03 AM
Hello,
string properties of BACnet objects can be modified from IEC code or via Modbus in case they are published also through this protocol, they can't be modified from BACnet BMS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-05 01:03 AM
Hello,
string properties of BACnet objects can be modified from IEC code or via Modbus in case they are published also through this protocol, they can't be modified from BACnet BMS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-07 11:31 PM
BACnet requires UTF-8 chars while M172 and IEC code supports ASCII from Programming, so the only way to be compliant with BTL is to have read only strings from BACnet side
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of