New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
M172P All-In-One USB Stick
HVAC and Pumping Forum
Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-2412:32 PM
M172P All-In-One USB Stick
Greetings!
It is useful to clarify one moment in creating "all-in-one" USB programming stick for M172P. Is there any parity in uploading files if I put both firmware and program files in same USB?
There are 2 expected behaviors (described in short):
1. (most likely) 2 cycles : Insert USB - upload firmware - reinsert USB - upload prog - BINGO! 2. (best for use) 1 cycle: insert USB - upload firmware - upload prog - remove usb - BINGO! 3. (unexpected) I have to use 2 different USB's.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-2712:02 AM
Hi,
for M172 we are in the case 3, M172 searches first for a bios so this has the priority (and after fw update M172 reboot so it will find again a bios update...).
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-2712:02 AM
Hi,
for M172 we are in the case 3, M172 searches first for a bios so this has the priority (and after fw update M172 reboot so it will find again a bios update...).