Posted: ‎2023-09-16 10:05 PM
2216
I want to connect PT 100, 3 wire to M172. Pls, help me configure AI and make an analog input register that can read from the Modbus pool. Many thanks
  • HVAC
Bastian_Schmitz
Champion
Posted: ‎2023-09-17 10:50 PM
2196
PT100 is not supported through M17x .
The TM17x Series support only Temp probes with higher resistence values.
Like PT1000 NTC (20kOhm) or PTC.
I would suggest you use one of these Types.
If a PT100 is mandotory for you. Please check the Harmony Analog converters from Schneider Electric.
Khoa_NTM
Khoa_NTM
Explorer
Posted: ‎2023-09-21 10:03 AM
In response to Bastian_Schmitz
I use the transmitter PT100 converter to output 4-20mA. (code: Seneca K120 RTD)
But the transmitter has no power supply. That means it must be connected to the PLC-type passive.
Please tell me how to connect the 4-20mA passive type to PLC M172. If yes, help me clear the blue area is a 4-20mA active type connection. The red area is a 4-20mA passive type, right?
Bastian_Schmitz
Champion
Posted: ‎2023-09-25 10:48 PM
Hi, yes use the red one to connect the converter