FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
EcoStruxure™ Machine Expert - HVAC
otrotabi
otrotabi
Contributor
Posted: ‎2023-01-02 09:08 AM
1437
Image blink TM172
Is it possible to make an image blink with HMI logic? For example, if compressor is OFF because Compressor OFF timer is running (but the compressor would start if not) I could make a logic like this:
xCompWillStart := CompCtrl_OnOFF.xCommand AND ReadWordBit(CompCtrl_OnOff_udiCompMgmtStatus,29);
(I am making some simplifications here just to show the concept, I know this does not work like it is written here)
Then if I am developing for M171 I could write :
IF CompCtrl_onOff.xCompCommand
    sysLocalLeds[6] := 1 ;
ELSIF xCompWillStart THEN
      sysLocalLeds[6] := 2 ;
ELSE
      sysLocalLeds[6] := 0 ;
END_IF;
I know I could generate a PLC logic to change a Status variable from TRUE to FALSE and eventually use that variable to handle the image visibility on the PLC but it demands some extra work at logic development.
I read about animation and image lists (I never actually used them) but it seems to be a similar concept, either one image or another would be displayed depending on the value of an animation variable.
I hope you get the idea of what I am looking for.
  • HVAC
  • Ecostruxure HVAC
  • TM172
Bastian_Schmitz
Champion
Posted: ‎2023-01-02 09:25 AM
1432
You could solve this via a procedur in the HMI part together with the systimer.
At first you need to create a blinker with the system Timer.
Then you could use the BOOL Output of this blinker to change the visibliltiy of the object in a defind ryhtem.
(like 1s)
I would expect that you could find an example in one of the integrated TVDAs.
Bastian_Schmitz
Champion
1433
(like 1s)
otrotabi
otrotabi
Contributor
Posted: ‎2023-01-02 10:03 AM
In response to Bastian_Schmitz
Thanks. You solved my main doubt, I thought I might be missing an easier solution.
I will check the TDVAs.