Posted: 2021-05-21 05:28 AM
I get an INT64 value, through Modbus TCP from a power meter, in four %IW (%IW68, %IW69, %IW70, %IW71).
My question is how could I merge these four input words to a value? I have seen here that LWORD type exists, but I couldn't find a function, like WORD_AS_DWORD, to merge my input values into a value. How could I do this?
I am using a TM251MESE PLC.
Many thanks in advance!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-21 06:24 AM . Last Modified: 2021-05-21 06:25 AM
Hi @jhonut ,
I believe you could try to create a %ML variable type LWORD to overlap those registers. Something like this:
And you can use in your program the %ML variable created.
I am not sure if inside Machine Expert we have function WORD_AS_LREAL or similar 🤔
Best regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-21 06:36 AM
Thanks for reply, @LeTomas!
I have searched in LibraryManager for WORD_AS_LREAL or DWORD_AS_LREAL, but I didn't find anything. I will try to use LWORD as you suggested.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-21 02:32 PM . Last Modified: 2021-05-21 02:38 PM
You could do it with localized variables %MW and %ML however you have to be careful about the position of the variables and that it's not used anywhere else.
I would typically use pointers instead. I do it in 2 lines of structured text. You could also embed that in a custom function that you would call in your program in any language.
Here is the function that you can import:
I declare a variable that is the array of 4 words and a variable that will be the destination 64bit LINT.
I also declare a pointer to LINT that will be the address location of my LINT variable. This location is automatically calculated at the time the project is built.
With this line " pLint := ADR(arWord1); " , I grab the address location of the word array and move it to my long int pointer.
In the next line " liLongInt1 := pLint^; " , I dereference the pointer with the ^ symbol. It extracts the value from the address location contained in the pointer.
VAR
arWord1 : ARRAY[0..3] OF WORD;
liLongInt1 : LINT;
pLint : POINTER TO LINT;
END_VAR
pLint := ADR(arWord1);
liLongInt1 := pLint^;
Link copied. Please paste this link to share this article on your social media post.