Can Communication troubleshooting

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • Can Communication troubleshooting
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Captain FedericoM Captain
90
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
55
LeTomas
Lt. Commander LeTomas Lt. Commander
14
M_Cervati
M_Cervati Support
12
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Machine Expert - HVAC

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to HVAC and Pumping Forum
Start a Topic
otrotabi
Commander otrotabi
Commander

Posted: ‎2023-02-02 07:00 AM

0 Likes
0
751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-02 07:00 AM

Can Communication troubleshooting

We have two chillers which are connected using CAN binding with TM172PDG18R controllers.  I set up communication following the attached tutorial.

 

Both chillers have exactly the same program, so the binding table is exactly alike as defined at HVAC installer.  I added some variables to both tables and at some point, I could no longer see one of the variables from PLC Node #1. Only one of them from a list of nine variables.

 

To make a long story short, I decided to start from scratch and followed the same procedure again from zero except that my binding table consists of only three variable now.

 

I can see some variables from from  PLC #2 on PLC #1 but not from the PLC #1 on PLC #2.

 

So far I have : 

 

1) Made sure both PLCs have the same program.

2) Made sure I downloaded the binding table to each PLC

3) Checked physical wiring. From both sides I can read 120 Ohm between + and - 

 

I am running out of ideas actually. What else can I try ?

 

EDIT .....

 

Tried for the nth. time and it seems to be working now again. However, I did not learn what might have gone wrong. Is it likely to start failing like this or definitively I f..d up somewhere ? 

 

Attachments
Labels
  • Labels:
  • HVAC
  • Tags:
  • Ecostruxure HVAC
  • english
  • TM172
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore