ATV320 EDM using DQ output
Hi,
I want to set up the STO function on the ATV320 inverter. I need to use the External device monitoring to achieve Cat4 safety requirement. There doesn't seem to be a dedicated EDM output, can the DQ+, DQ- be used as EDM feedback?
- Labels:
-
Safety
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-25 04:58 AM
Hi,
We can configure the output DQ as feedback from the STO. A screenshot of SoMove and the Safety functions manual, which contains wiring diagrams according to Safety CAT, are attached
.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-25 04:58 AM
Hi,
We can configure the output DQ as feedback from the STO. A screenshot of SoMove and the Safety functions manual, which contains wiring diagrams according to Safety CAT, are attached
.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-28 02:16 AM
Hi, thanks for the feedback it was very helpful. I didn't initally see the feedback options for the DQ assignement. I see the "power removal state" is the correct selection.
Thanks