Alarms in Geo SCADA can be redirected to SMS messages and may be acknowledged via an SMS response. Getting this functionality to work however requires care. The purpose of this article is to point out some general information on getting this feature working.
This list is of devices that have been noted as working, and is not exhaustive
For a modem to work it must support at a minimum GSM 07.07/3GPP TS 27.007 AT command set.
In addition, prior to ClearSCADA 2015 R1 the modem MUST support "AT+CNMI=3,2" if it is used to receive incoming SMS messages. ClearSCADA 2015 R1 onwards and all versions of Geo SCADA also supports other CNMI modes. The modes supported by a modem can be queried using the "AT+CNMI=?" command (without the quotes) from a VT terminal.
Also, all drivers in Geo SCADA require that the modem be configured with verbose result codes enabled (V1), not numeric result codes (V0), and echo disabled (E0) not enabled (E1). The default modem command for pager channels is "ATV1E0H0S0=0".
For SMS alarms to work correctly a GSM standalone modem MUST be used. Sending SMS via E-Mail will fail in most cases.
Generally speaking the basic configuration in Geo SCADA is as follows:
There are a few common stumbling blocks associated with this sort of setup.
SMS IO.PNGSMS IO.PNG