DBServer Log Analysis

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • DBServer Log Analysis
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 03:58 PM
0 Likes
0
1043
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 03:58 PM

DBServer Log Analysis

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 10, 2021 12:58 AM

📖 Home  Back  
All ClearSCADA log entries follow the same pattern as below:
15-FEB-2010 15:27:59.683 0224 [OPCAEEVENTMGT] 1:05 GetState( IN )

  • UTC Date Time

  • Thread Id (HEX)

  • Identifier

  • Message


Here is an example log excerpt:
15-FEB-2010 15:27:59.683 0224 [OPCAEEVENTMGT] 1:05 GetState( IN )

15-FEB-2010 15:27:59.683 0224 [OPCAEEVENTMGT] 1:05 GetState( OUT: hr 0 -> Ok.)

15-FEB-2010 15:27:59.684 0464 [OPCAE] 2:02 GetStatus( OUT: hr 0 -> Ok.)

15-FEB-2010 15:28:00.003 0C7C Perform DoMinuteOp() on objects

15-FEB-2010 15:28:00.003 0C7C DoMinuteOp() on objects complete

15-FEB-2010 15:28:00.003 0C7C Calculate object memory usage (starting offset 0)

15-FEB-2010 15:28:00.003 0C7C Calculate object memory usage complete

15-FEB-2010 15:28:00.003 06C8 [DBFILE]  PerformSave next state Metadata.

15-FEB-2010 15:28:00.003 06C8 [DBFILE]  About to save metadata

15-FEB-2010 15:28:00.003 06C8 [DBFILE]  PerformSave next state Structure.

15-FEB-2010 15:28:00.003 06C8 [DBFILE]  About to save structure

15-FEB-2010 15:28:00.003 06C8 [DBFILE]  PerformSave next state Permit.

15-FEB-2010 15:28:00.003 06C8 [DBFILE]  About to save permit

15-FEB-2010 15:28:00.003 06C8 [DBFILE]  PerformSave next state Config.

15-FEB-2010 15:28:00.003 06C8 [DBFILE]  About to save config

15-FEB-2010 15:28:00.004 06C8 [DBFILE]  Config save (no changes)

15-FEB-2010 15:28:00.004 06C8 [DBFILE]  PerformSave next state Data.

15-FEB-2010 15:28:00.004 06C8 [DBFILE]  About to save data

15-FEB-2010 15:28:00.004 06C8 [DBFILE]  Data save (no changes)

15-FEB-2010 15:28:00.004 06C8 [DBFILE]  No database changes detected, nothing saved

15-FEB-2010 15:28:00.004 06C8 [DBFILE]  PerformSave next state Idle.

15-FEB-2010 15:28:02.375 0270 [SVRADVTHR] 1 Timeout

15-FEB-2010 15:28:02.375 1280 [SVRTHR] 1 Timeout

15-FEB-2010 15:28:02.376 0464 [SVRTHR] 2 Timeout

15-FEB-2010 15:28:02.376 0D7C [SVRADVTHR] 2 Timeout

15-FEB-2010 15:28:02.398 13C8 [DATAFILE]  Beginning flush cycle

15-FEB-2010 15:28:02.398 13C8 [DATAFILE]  Flush cycle complete, flushed 0 files (0 bytes), time taken 0.000000 milliseconds

15-FEB-2010 15:28:02.532 0F0C [ICMP]  Poll Timer Callback

15-FEB-2010 15:28:02.532 0F0C [ICMP]  Tx 0: Addr 172.24.1.204 (172.24.1.204), Len 40, Ident 256, Seq 143

15-FEB-2010 15:28:03.745 1280 [SCXIcon]  1:01 Poll()

15-FEB-2010 15:28:11.739 1194 [SVR]  Accepted connection 14 from 127.0.0.1:50880 to 127.0.0.1:5481...

15-FEB-2010 15:28:11.739 1194 [SVR]  ... Connection 14: Type 1, client version 0x6450E64 (6.69.3684), (Uncompressed,Floating Licence,ViewX,Include Checksums)

15-FEB-2010 15:28:11.739 1194 [SVR]  ... Connection 14 confirmed, link version 6.69.3684, client name 'IP 127.0.0.1, Session 1'

15-FEB-2010 15:28:11.740 1194 [SVRTHR] 1 AddClient from 127.0.0.1:50880, link is [SCX]  1:10

15-FEB-2010 15:28:11.740 1194 [SCX] 1:10 QP Created

15-FEB-2010 15:28:11.740 1280 [SCX] 1:10 SetClientDetails( IN: LoggedOn 0, User (null), Workstation Name , Client Name Unknown )

15-FEB-2010 15:28:11.740 1280 [SCX] 1:10 SetClientDetails( OUT: Hr 0 -> Ok. )

15-FEB-2010 15:28:11.740 1280 [SCX] 1:10 SetClientDetails( IN: Lcid 0x809, ClientName STEFAN-W7::CSCXObject)

15-FEB-2010 15:28:11.740 1280 [SCX] 1:10 SetClientDetails( OUT: Features 19727, hr 0 -> Ok. )

15-FEB-2010 15:28:11.741 0224 [SCX] 1:10 FindObject( IN: Name 'New Analogue Point' )

15-FEB-2010 15:28:11.741 0224 [SCX] 1:10 FindObject( OUT: Id 1, Hr 0 -> Ok. )

15-FEB-2010 15:28:11.752 0224 [SCX] 1:10 ReadObject( IN: Id 1 )

15-FEB-2010 15:28:11.766 0224 [SCX] 1:10 ReadObject( OUT: hr 0 -> Ok., Version 1, Count 7 )


Thread ID


The Thread ID can be used to identify which thread created the log entry.
A list of all threads indexed by Thread ID can be found in
  • Server Status, General/Threads tab

  • The 'General Threads' section of DB_SNAPSHOT file


Identifier


The Identifier may indicate the component of DBServer that logged the message, [DBFILE] below:
15-FEB-2010 15:28:00.003 06C8 [DBFILE]  PerformSave next state Metadata.

15-FEB-2010 15:28:00.003 06C8 [DBFILE]  About to save metadata

15-FEB-2010 15:28:00.003 06C8 [DBFILE]  PerformSave next state Structure.

15-FEB-2010 15:28:00.003 06C8 [DBFILE]  About to save structure

15-FEB-2010 15:28:00.003 06C8 [DBFILE]  PerformSave next state Permit.


It may also indicate the link used by a remote client to communicate with the server. The following message were raised from link '[SCX] 1:10', link type 'SCX' and id '1:10':
15-FEB-2010 15:28:11.741 0224 [SCX] 1:10 FindObject( IN: Name 'New Analogue Point' )

15-FEB-2010 15:28:11.741 0224 [SCX] 1:10 FindObject( OUT: Id 1, Hr 0 -> Ok. )

15-FEB-2010 15:28:11.752 0224 [SCX] 1:10 ReadObject( IN: Id 1 )

15-FEB-2010 15:28:11.766 0224 [SCX] 1:10 ReadObject( OUT: hr 0 -> Ok., Version 1, Count 7 )


Details about the system's active links can be accessed via
  • Server Status, On the Server/Links tab

Server Links.pngServer Links.pngServer Links.png
  • The 'Server Links' section of DB_SNAPSHOT files


Amongst other things the client connection id can be used to identify:
  • Source, IP Address

  • Client Version/Effective Link Version, ClearSCADA Version

  • Client Name, Name of the machine (or driver)

  • User Name, ClearSCADA user


Example Analysis



In this example we can follow the activity associated with a new client link that connected to the server.

15-FEB-2010 15:28:11.739 1194 [SVR]  Accepted connection 14 from 127.0.0.1:50880 to 127.0.0.1:5481...

15-FEB-2010 15:28:11.739 1194 [SVR]  ... Connection 14: Type 1, client version 0x6450E64 (6.69.3684), (Uncompressed,Floating Licence,ViewX,Include Checksums)

15-FEB-2010 15:28:11.739 1194 [SVR]  ... Connection 14 confirmed, link version 6.69.3684, client name 'IP 127.0.0.1, Session 1'

'[SVR]' logs the new incomming connection recording the connection details (source and destination IP addresses and ports).
The client version, licensing details and client name are identified.

15-FEB-2010 15:28:11.740 1194 [SVRTHR] 1 AddClient from 127.0.0.1:50880, link is [SCX]  1:10

'[SVRTHR] 1' adds the client and assignes it the link identifier '[SCX] 1:10'. (For details on links and link threads see Links, Advises and Associated Server Threads)

15-FEB-2010 15:28:11.740 1194 [SCX] 1:10 QP Created

15-FEB-2010 15:28:11.740 1280 [SCX] 1:10 SetClientDetails( IN: LoggedOn 0, User (null), Workstation Name , Client Name Unknown )

15-FEB-2010 15:28:11.740 1280 [SCX] 1:10 SetClientDetails( OUT: Hr 0 -> Ok. )

15-FEB-2010 15:28:11.740 1280 [SCX] 1:10 SetClientDetails( IN: Lcid 0x809, ClientName STEFAN-W7::CSCXObject)

15-FEB-2010 15:28:11.740 1280 [SCX] 1:10 SetClientDetails( OUT: Features 19727, hr 0 -> Ok. )

15-FEB-2010 15:28:11.741 0224 [SCX] 1:10 FindObject( IN: Name 'New Analogue Point' )

15-FEB-2010 15:28:11.741 0224 [SCX] 1:10 FindObject( OUT: Id 1, Hr 0 -> Ok. )

15-FEB-2010 15:28:11.752 0224 [SCX] 1:10 ReadObject( IN: Id 1 )

15-FEB-2010 15:28:11.766 0224 [SCX] 1:10 ReadObject( OUT: hr 0 -> Ok., Version 1, Count 7 )

We now see details about the activity of '[SCX] 1:10' as its connection is initialised and client details registered.
The client then finds the object 'New Analogue Point' to determine its Object Id, in this case '1'.
The client then reads the details of Object Id 1.

Go: Home Back

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore