Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Connecting ClearSCADA to MicroLogix 1500 using DF1 via Serial Cable

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • Connecting ClearSCADA to MicroLogix 1500 using DF1 via Serial Cable
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 05:00 PM
0 Likes
0
1496
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 05:00 PM

Connecting ClearSCADA to MicroLogix 1500 using DF1 via Serial Cable

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 10, 2021 02:00 AM

📖 Home  Back  
Connecting ClearSCADA to MicroLogix 1500 using DF1 via Serial Cable.


Descriptions:
ClearSCADA DF1 serial drivers does not communicate MicroLogix DF1 protocol. Thus, ClearSCADA DF1 communicates PLC2, PLC3, PLC5, PLC5/250, and SLC500 (see below PLC Type selection from ClearSCADA).
worddavb9e6eb3203fe3c3d17a521eccaf1ad03.pngworddavb9e6eb3203fe3c3d17a521eccaf1ad03.pngworddavb9e6eb3203fe3c3d17a521eccaf1ad03.png


In order to successfully communicate with the MicroLogix 1500 would required KEPServerEX (integrated PLC drivers in ClearSCADA). This forum will go through the steps to configure PLC Drivers in ClearSCADA to communicate DF1 with MicroLogix 1500 PLC.


Configuring ClearSCADA to communicate to Micrologix 1500 via DF1 through RS-232 serial cable.


In this demo setup from PC running ClearSCADA Server, the followings:
Using COM4 on PC to connect to the Channel 1 on the MicroLogix 1500. Null modem RS232 serial cable is connected from PC COM4 to Channel 1 of Micrologix 1500 (3 wires).


Note: ClearSCADA must have PLC License in order to use the built-in KEPServerEX for ClearSCADA to communicate DF1 with MicroLogix 1500.
worddav4a140fe77d22665801c3aba6ad52a65a.pngworddav4a140fe77d22665801c3aba6ad52a65a.pngworddav4a140fe77d22665801c3aba6ad52a65a.png



Setup in Allen Bradley MicroLogix 1500 using RSLogix 500:


Step 1:
Set up Channel 1 with Driver DF1 Half Duplex Slave and enter the Node Address 20, Baud 19200, Parity None, and CRC. Protocol Control has "No Handshaking" and Enable "EOT Suppression" .
worddavfd40f48ff1681d46b8eb4c633bd23ae5.pngworddavfd40f48ff1681d46b8eb4c633bd23ae5.pngworddavfd40f48ff1681d46b8eb4c633bd23ae5.png



Step 1:
Using Windows Explorer, browse to folder C:\Program Files\Control Microsystems\ClearSCADA\KEPServerEX
worddav2a4a60b959676de13bbb1f4f1634342c.pngworddav2a4a60b959676de13bbb1f4f1634342c.pngworddav2a4a60b959676de13bbb1f4f1634342c.png



Step 2: Open up the ServerMain.exe
worddav2dd2a2cd42e55d959b4637a75434ed33.pngworddav2dd2a2cd42e55d959b4637a75434ed33.pngworddav2dd2a2cd42e55d959b4637a75434ed33.png



Step 3: Once KEPServerEX for ClearSCADA opens up go to the menu and choose File --> New

worddava76e32e37a2197b19507307603a8f883.pngworddava76e32e37a2197b19507307603a8f883.pngworddava76e32e37a2197b19507307603a8f883.png



Step 4: Double-Click to add Channel to communicate from PC to the MicroLogix PLC.
worddav4a41f3a34d64c08e7ecb1a5e454ae113.pngworddav4a41f3a34d64c08e7ecb1a5e454ae113.pngworddav4a41f3a34d64c08e7ecb1a5e454ae113.png



Step 5: Set the Device Driver to DF1.
worddavc3cff607b20314629314eb3225dd4ce5.pngworddavc3cff607b20314629314eb3225dd4ce5.pngworddavc3cff607b20314629314eb3225dd4ce5.png



Step 6: Select the Serial COM port from the PC that would be used to connect to the MicroLogix 1500 PLC.
worddav94f92759ea3f8fc685f237da1e94a268.pngworddav94f92759ea3f8fc685f237da1e94a268.pngworddav94f92759ea3f8fc685f237da1e94a268.png



Step 7: Leave the settings as default, press Next.
worddav2cc331dbe2391c2f92b655e7a0bdeddf.pngworddav2cc331dbe2391c2f92b655e7a0bdeddf.pngworddav2cc331dbe2391c2f92b655e7a0bdeddf.png



Step 8: Select Half Duplex Master. This matches the settings on the PLC when it was set to be Half Duplex Slave.
worddavfc87d359ab7e7cb72cc9810a9375741c.pngworddavfc87d359ab7e7cb72cc9810a9375741c.pngworddavfc87d359ab7e7cb72cc9810a9375741c.png
worddav0256e5d5e9289249a44964265ef13d85.pngworddav0256e5d5e9289249a44964265ef13d85.pngworddav0256e5d5e9289249a44964265ef13d85.png



Step 9: Review the settings made, press Finish.
worddav95d18c772fe8f7617458c1721f2f7458.pngworddav95d18c772fe8f7617458c1721f2f7458.pngworddav95d18c772fe8f7617458c1721f2f7458.png

Step 10: Double click to add a device under channel created. Rename to Micrologix 1500 test.
worddavc0bcdbd3053e5db191b54f5774dcaa48.pngworddavc0bcdbd3053e5db191b54f5774dcaa48.pngworddavc0bcdbd3053e5db191b54f5774dcaa48.png

Step 11: Select MicroLogix from Device model.
worddav06532dc141c24635302831724661dc05.pngworddav06532dc141c24635302831724661dc05.pngworddav06532dc141c24635302831724661dc05.png

Step 12: Enter in Device ID = 20, this number is entered from Allen Bradley RS500 setup earlier.
worddav542d7e3dbd488ba09cac073bb12690e7.pngworddav542d7e3dbd488ba09cac073bb12690e7.pngworddav542d7e3dbd488ba09cac073bb12690e7.png

worddave34dd9aa8baefb13f76ed5fef44d5716.pngworddave34dd9aa8baefb13f76ed5fef44d5716.pngworddave34dd9aa8baefb13f76ed5fef44d5716.png



Step 13: Press Next, leave as default.
worddav3389372f583230677fbfb6eda0b037c0.pngworddav3389372f583230677fbfb6eda0b037c0.pngworddav3389372f583230677fbfb6eda0b037c0.png

Step 14: Press Next, leave as default.
worddavc32991ff75c0d42a7a7ca5aa2010b5e5.pngworddavc32991ff75c0d42a7a7ca5aa2010b5e5.pngworddavc32991ff75c0d42a7a7ca5aa2010b5e5.png

Step 15: Using CRC and Request Size Large. This is default, press Next.
worddav59aecb65a319de0bb4ed9d3eb8b7dc2c.pngworddav59aecb65a319de0bb4ed9d3eb8b7dc2c.pngworddav59aecb65a319de0bb4ed9d3eb8b7dc2c.png

Step 16: Leave as default and press Next.
worddave7e0f7947d53863f92dfa8ea733019f5.pngworddave7e0f7947d53863f92dfa8ea733019f5.pngworddave7e0f7947d53863f92dfa8ea733019f5.png

Step 16: Click on Finish.
worddav35db4a12e76a34e12c7dbbbf06507ec2.pngworddav35db4a12e76a34e12c7dbbbf06507ec2.pngworddav35db4a12e76a34e12c7dbbbf06507ec2.png

Step 17: Double click on right side panel to add in Tag.
worddavcc6af538983dcff72fa5d13783ba9dde.pngworddavcc6af538983dcff72fa5d13783ba9dde.pngworddavcc6af538983dcff72fa5d13783ba9dde.png

Step 18: Repeat step 17 and would get a table like below screen.
worddav86fba8de8497ae5fb2ec0fab8f90746b.pngworddav86fba8de8497ae5fb2ec0fab8f90746b.pngworddav86fba8de8497ae5fb2ec0fab8f90746b.png





Save the project in KEPServerEX and close this application. Next is to configure ClearSCADA to get the values from these points using ClearSCADA PLC Driver.







Setting up ClearSCADA to use PLC Drivers to communicate with MicroLogix 1500 via KEPServerEX.


Step 1: Create a new Group for "MicroLogix 1500 test". Then add new PLC  Scanner object to this group.


Note: Right mouse click on Main to add in new Group, then also right mouse click to add in new PLC --> Scanner.

worddave7485f0afb53fb53e2b331f2f3235486.pngworddave7485f0afb53fb53e2b331f2f3235486.pngworddave7485f0afb53fb53e2b331f2f3235486.png

Step 2: Open up the properties of the Scanner to set the Scan Rate interval. Default is 5S, 5 second.
worddavaef2ced1d2aea29ec4b8254a8d6b5a6d.pngworddavaef2ced1d2aea29ec4b8254a8d6b5a6d.pngworddavaef2ced1d2aea29ec4b8254a8d6b5a6d.png



Step 3: Right mouse click on "Micrologix 1500 test" group and choose New PLCDigital Point.
worddav2f8298df30a4852e286f5e9e1da65c44.pngworddav2f8298df30a4852e286f5e9e1da65c44.pngworddav2f8298df30a4852e286f5e9e1da65c44.png

Step 4: Rename New Digital Point to "Input 0" and double click to open up the properties. Click on PLC tab, configure the Scanner press "..." button and attach the "MicroLogix 1500 test.Scanner" object.
worddav8ec36b4d502e9534ee3d2b7e0fec1ac5.pngworddav8ec36b4d502e9534ee3d2b7e0fec1ac5.pngworddav8ec36b4d502e9534ee3d2b7e0fec1ac5.png

Step 6: Attach the Tag Name next, click on "..." button and browse to open up the Tag list and select Input 0 shown.
worddavea5d5cabde7b38b8c405f41f91b0deee.pngworddavea5d5cabde7b38b8c405f41f91b0deee.pngworddavea5d5cabde7b38b8c405f41f91b0deee.png

Step 7: Click on Historic tab and click on Enable. This would allow ClearSCADA to log all the point updates.
worddav1f4e87c2bf0f3b9eb47c580d9ea69094.pngworddav1f4e87c2bf0f3b9eb47c580d9ea69094.pngworddav1f4e87c2bf0f3b9eb47c580d9ea69094.png

Checking for point value update Right mouse click on the Input 0 in database and choose View Status
worddav42e3c000f6dbbe4f9dad0fad756c3350.pngworddav42e3c000f6dbbe4f9dad0fad756c3350.pngworddav42e3c000f6dbbe4f9dad0fad756c3350.png



Step 7: In order to get the other number such as Float, add New -->PLC--> Analog Point
worddavd3946c6cf759eea7257936009fc50189.pngworddavd3946c6cf759eea7257936009fc50189.pngworddavd3946c6cf759eea7257936009fc50189.png

Step 8: Rename the New Analog Point to N7_0. Double click to open the properties then browse to PLC tab. Attach the Scanner to link to "MicroLogix 1500 test.Scanner" from "..." button. Click on "..." on Tag Name and attach the IntegerN7_0 tag.
worddavc85106d00aecf2c7c6ca752be63b3b08.pngworddavc85106d00aecf2c7c6ca752be63b3b08.pngworddavc85106d00aecf2c7c6ca752be63b3b08.png

Note: Click on Historic and Enable to have ClearSCADA log the updates.
Verify the N7_0 point value polling status.
worddav42a887b74ceff83cd80ba0484d8633df.pngworddav42a887b74ceff83cd80ba0484d8633df.pngworddav42a887b74ceff83cd80ba0484d8633df.png worddav63df4e1b6bd2b5de5cffa81daf8877a5.pngworddav63df4e1b6bd2b5de5cffa81daf8877a5.pngworddav63df4e1b6bd2b5de5cffa81daf8877a5.png





worddav10724f23f3d04cd4488f976aa132b449.pngworddav10724f23f3d04cd4488f976aa132b449.pngworddav10724f23f3d04cd4488f976aa132b449.png

Step 10: Repeat adding in the ClearSCADA PLC points for all the Tags created in KEPServerEX.

Sample files can be download below:

File: AUTOMATE.RSS (See links below) (RSLogix 500 file)

File: MicroLogix 1500 Test.sde (See links below) (ClearSCADA Import file)

File: micrologix1500.opf (See links below) (ClearSCADA integrated KEPServerEX project file)

File: MicroLogix1500_CS.otc (See links below) (ClearSCADA integrated KEPServerEX project file)


Go: Home Back
MicroLogix 1500 Test.sde

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore