Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

ClearSCADA 2010 R1 Upgrade Notes

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • ClearSCADA 2010 R1 Upgrade Notes
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 09:39 AM
0 Likes
0
744
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 09:39 AM

ClearSCADA 2010 R1 Upgrade Notes

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 09, 2021 06:39 PM

📖 Home  Back  
Please read the information below prior to upgrading to ClearSCADA 2010 R1 for important information on changes in this version.

Upgrading from ClearSCADA 2009 R2.x



  • ClearSCADA 2010 R1 includes support for Crystal Reports 2008. When upgrading an existing Crystal Report installation to Crystal Reports 2008, please note the following:

  • Grouped Boolean parameters are not supported in Crystal Reports 2008 and will be displayed in the parameters dialog as a number of normal boolean checkboxes. A way to work around this issue is to use a numeric parameter with a discrete list of values which will be presented in the dialog as a combo box, and using conditional statements to reference the parameter in queries.

  • The following export formats are no longer supported:

  • Record Format

  • ODBC export

  • "Lotus Domino" is no longer supported as an export destination.


  • ClearSCADA 2010 R1 utilises the Crystal Reports XI Release 2 Service Pack 6 runtime. To maximise compatibility we recommend upgrading all associated Crystal Reports installations to Crystal Reports XI Release 2 Service Pack 6.


  • Following upgrade to ClearSCADA 2010 R1, all existing ODBC DSNs will lose their passwords. This potentially impacts report generation using Crystal Reports and external applications that use the ODBC driver. Hence, after upgrade, use the ODBC Data Source Administrator to reinstate ODBC DSN passwords. This applies to upgrade from all versions with the exception of ClearSCADA 2009 R2.2, ClearSCADA 2009 R1.3 and ClearSCADA 2007 R1.4.


Upgrading from ClearSCADA 2009 R1.x


Please be aware of all the issues covered in the section "Upgrading from ClearSCADA 2009 R2.x" in addition to the following.

  • The "Deadband" and "Persistence" properties have been removed from the Driver Development Kit "PointSourceEntry" class as they are not relevant. This will cause existing DDK programs to fail to compile if they make use of these removed items. Hence before compiling any DDK programs, ensure that these properties are not used in the programs.


Upgrading from ClearSCADA 2007 R1.x


Please be aware of all the issues covered in the sections "Upgrading from ClearSCADA 2009 R1.x" and "Upgrading from ClearSCADA 2009 R2.x" in addition to the following.

  • There is a known issue when instantiating particular types of objects within templates when running a mixed version redundant pair that could potentially result in an Integrity Check failure. It is recommended that minimal database changes be made during mixed version redundant pair operation and that servers are not run in this mode for extended periods of time.

  • Upgrading from older versions of ClearSCADA to ClearSCADA 2010 R1 requires a new version 6 license to be issued. The older version 5 license will give an error if used on a machine running the ClearSCADA 2010 R1 version.

  • Older versions of ClearSCADA contained a section in the Server Configuration tool called "User Contact Details" which allowed some of the fields associated with a user object such as E-Mail Address and Pager Id to be renamed. This section has been removed from the Server Configuration tool in ClearSCADA 2010.

Editing the names of database fields this way creates some entries in the "Metadata" key at the following location "HKEY_LOCAL_MACHINE\SOFTWARE\Serck Controls\SCX6\Metadata" in the Registry. The entries will look like one of the following depending on the field that has been renamed.
  • Field_CDBUserContactConfig_EmailAddress

  • Field_CDBUserContactConfig_EmailAddress2

  • Field_CDBUserContactConfig_EmailAddress3

  • Field_CDBUserContactConfig_EmailAddress4

  • Field_CDBUserContactConfig_TextOnly

  • Field_CDBUserContactConfig_TextOnly2

  • Field_CDBUserContactConfig_TextOnly3

  • Field_CDBUserContactConfig_TextOnly4

  • Label_CDBUserContactConfig_EmailAddress

  • Label_CDBUserContactConfig_EmailAddress2

  • Label_CDBUserContactConfig_EmailAddress3

  • Label_CDBUserContactConfig_EmailAddress4

  • Field_CDBUserContactConfig_PagerId

  • Field_CDBUserContactConfig_PagerId2

  • Field_CDBUserContactConfig_PagerId3

  • Field_CDBUserContactConfig_PagerId4

  • Field_CDBUserContactConfig_PagerServiceId

  • Field_CDBUserContactConfig_PagerServiceId2

  • Field_CDBUserContactConfig_PagerServiceId3

  • Field_CDBUserContactConfig_PagerServiceId4

  • Label_CDBUserContactConfig_PagerId

  • Label_CDBUserContactConfig_PagerId2

  • Label_CDBUserContactConfig_PagerId3

  • Label_CDBUserContactConfig_PagerId4

Before upgrading databases containing these renamed fields, these entries must be removed from the Metadata registry key. Otherwise, after the upgrade when the server is started, the Server Icon will go purple with "Invalid Metadata" error. By removing these registry values, the rename functionality will be disabled while maintaining the data associated with these points.


  • In ClearSCADA 2010 R1, the Snapshot filename has been changed from "DB_Snapshot_" to "DBSnapshot_". To ensure that the appropriate number of Snapshot files are generated, please update the settings in the registry key HKEY_LOCAL_MACHINE\SOFTWARE\Serck Controls\SCX6\DBSnapshot.

  • The older versions of ClearSCADA allowed Ethernet 1 or 2 to be selected as the DNP3 Master Port in the settings for DNP3 outstations even though the TCP/IP option was not enabled on the outstation. This is invalid configuration and has been fixed in ClearSCADA 2010. When upgrading to ClearSCADA 2010 from older versions, the outstations having this invalid configuration will have errors on them with an error message displayed saying "Invalid DNP Master Port 5".To correct this, enable TCP/IP and enter valid IP addresses for the Ethernet settings.

  • In older versions of ClearSCADA, for a Channel with Connection Type set to "Network", an outstation could be configured with the "Network" field in the Network tab set to "None". This is invalid configuration and if a database containing this configuration is upgraded to ClearSCADA 2010, then configuration error is displayed on the outstation with the error message saying "Network Channel ... on set ... is not compatible with outstation.". To correct this error, a Network Type needs to be selected and the host address and port details need to be entered for the oustation.

  • Dial-In Line Settings for PSTN outstations:

  • In older versions of ClearSCADA, a PSTN Channel could be configured as "Dial In Only" or "Dial In and Dial Out" and there was no provision on the PSTN outstation form to specify the dial in channel settings. In ClearSCADA 2010, the PSTN tab for outstations has been modified so that the dial in line settings can be specifed. Hence, when upgrading from older versions of ClearSCADA to ClearSCADA 2010, if the PSTN Channel is specifed as "Dial In Only" or "Dial In and Dial Out", the status of the PSTN outstation will be "Available, Outgoing Only" unless the dial in channel details are specifed in the "Dial In Line Settings" of the PSTN outstation. Then the status of the outstation becomes "Available".

  • Changes in Port Configuration on E-Series Outstations:

  • In ClearSCADA 2010, port configurations for E-Series outstations have been moved into a multi-choice aggregate.

  • If you used automation interface code to configure port settings, then this code will no longer work in ClearSCADA 2010. Please use the example code below to modify your applications to use the new port structure.

ClearSCADA 2007 and earlier
Sub main()Dim objserver As ScxV6ServerDim obj As ScxV6ObjectDim sPort0DLRetries as StringSet objserver = New ScxV6Serverobjserver.Connect "MAIN", "", ""Set obj = objserver.FindObject("E-Series OS")'read the properties directlysPort0DLRetries = obj.Property("Port0DLRetries")End Sub

ClearSCADA 2009
Sub main()Dim objserver As ScxV6ServerDim obj As ScxV6ObjectDim aggOSType As ScxV6AggregateDim sPort0DLRetries as StringSet objserver = New ScxV6Serverobjserver.Connect "MAIN", "", ""Set obj = objserver.FindObject("E-Series OS")'Note that you need to find the board type aggregate before reading propertiesSet aggOSType = obj.Aggregate("BoardType")sPort0DLRetries = aggOSType.Property("Port0DLRetries")End Sub



Upgrading from an Older Version


Please be aware of all issues covered in the sections above.
Please also be aware of the Known Issues and Release Notes for each releases since the version of ClearSCADA that is being upgraded.

Older ClearSCADA Known Issues and Release Notes pages can be found in the Control Microsystems Resource Center.

Go: Home Back

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore