ClearSCADA 2007 R1 Upgrade Strategy

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • ClearSCADA 2007 R1 Upgrade Strategy
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Application Programming 12
  • Setup 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Support 5
  • IoT 5
  • SCADA 5
  • Geo SCADA Expert 5
  • Drivers and Communications 4
  • Security 4
  • DNP 3 3
  • IEC 61131-3 Logic 3
  • Trends and Historian 2
  • Virtual ViewX 2
  • Geo Scada 1
  • ClearSCADA 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Architectures 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • OPC UA - Driver and Server
  • Requirements for Generating a Valid OPC UA Server Certificate
  • Load Events Using LoadRecord and LoadRecords
  • Geo SCADA Embedded Component Licenses
  • Geo SCADA 2023 Known Issues
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 02:52 PM
0 Likes
0
575
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 02:52 PM

ClearSCADA 2007 R1 Upgrade Strategy

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 09, 2021 11:52 PM

📖 Home  Back  
Upgrading from previous versions of ClearSCADA to ClearSCADA 2007 R1 in a main/standby arrangement requires that both servers be shut down during the upgrade. The next version of ClearSCADA (ClearSCADA 2007 R1.1) will provide support for redundancy between R0 and R1.1 ensuring continuous operation during the upgrade process. If you plan to upgrade a system that cannot be shutdown for the few minutes during the upgrade, please use a later service pack for ClearSCADA 2007 R1 such as R1.1 or R1.2.

For details on version compatibility of clients and servers as well as server-server for redundancy, please refer to the ClearSCADA Version Compatibility Matrix.


ClearSCADA 2007 R0



ClearSCADA 2007 R0 Standalone Server


  • Shut the server down.

  • Upgrade the server to ClearSCADA 2007 R1.

  • Restart the server.


ClearSCADA 2007 R0 Main and Standby Servers with no Clients


  • Shut both the main and standby servers down.

  • Upgrade the main server to ClearSCADA 2007 R1.

  • Restart the main server.

  • If the main server has upgraded correctly, upgrade the standby server to ClearSCADA 2007 R1.

  • Restart the standby server.


Notes

  • It is important that the server that was the last to be shut down in a redundant pair is the first to be restarted to ensure that data received by this server is not overwritten by data from an older server.


ClearSCADA 2007 R0 Main and Standby Servers with Clients


If there are a small number of clients that can easily be upgraded:
  • Upgrade each client in turn to ClearSCADA 2007 R1.

  • Shut both the main and standby servers down.

  • Upgrade the main server to ClearSCADA 2007 R1.

  • Restart the main server.

  • If the main server has upgraded correctly, upgrade the standby server to ClearSCADA 2007 R1.

  • Restart the standby server.


If there are a large number of clients or clients that cannot easily be upgraded (due to location, availability, etc.):
  • Shut both the main and standby servers down.

  • Upgrade the main server to ClearSCADA 2007 R1.

  • Restart the main server.

  • Configure the main server to emulate ClearSCADA 2007 R0.

  • Restart the main server.

  • If the main server has upgraded correctly, upgrade the standby to ClearSCADA 2007 R1.

  • Restart the standby server.

  • Configure the standby server to emulate ClearSCADA 2007 R0.

  • Restart the standby server.

  • Upgrade each client in turn to ClearSCADA 2007 R1.


Notes

  • It is important that the server that was the last to be shut down in a redundant pair is the first to be restarted to ensure that data received by this server is not overwritten by data from an older server.

  • Once the ClearSCADA 2007 R0 emulation has been enabled on both the main and standby servers, either ClearSCADA 2007 R0 or R1 clients can be used to connect to the servers.

  • Once all of the clients have been upgraded to ClearSCADA 2007 R1, the ClearSCADA 2007 R0 emulation should be disabled on both the main and standby servers.

  • User favorites will not be accessible from non-ClearSCADA 2007 R1 clients.



ClearSCADA 2005 R1



ClearSCADA 2005 R1 Standalone Server


  • Shut the server down.

  • Upgrade the server to ClearSCADA 2007 R1.

  • Upgrade the ClearSCADA licence on the server.

  • Restart the server.


ClearSCADA 2005 R1 Main and Standby Servers with no Clients


  • Shut both the main and standby servers down.

  • Upgrade the main server to ClearSCADA 2007 R1.

  • Upgrade the ClearSCADA licence on the main server.

  • Restart the main server.

  • If the main server has upgraded correctly, upgrade the standby server to ClearSCADA 2007 R1.

  • Upgrade the ClearSCADA licence on the standby server.

  • Restart the standby server.


Notes

  • It is important that the server that was the last to be shut down in a redundant pair is the first to be restarted to ensure that data received by this server is not overwritten by data from an older server.



ClearSCADA 2005 R1 Main and Standby Servers with Clients


If there are a small number of clients that can easily be upgraded:
  • Upgrade each client in turn to ClearSCADA 2007 R1.

  • Shut both the main and standby servers down.

  • Upgrade the main server to ClearSCADA 2007 R1.

  • Upgrade the ClearSCADA licence on the main server.

  • Restart the main server.

  • If the main server has upgraded correctly, upgrade the standby server to ClearSCADA 2007 R1.

  • Upgrade the ClearSCADA licence on the standby server.

  • Restart the standby server.


If there are a large number of clients or clients that cannot easily be upgraded (due to location, availability, etc.):
  • Shut both the main and standby servers down.

  • Upgrade the main server to ClearSCADA 2007 R1.

  • Upgrade the ClearSCADA licence on the main server.

  • Restart the main server.

  • Configure the main server to emulate ClearSCADA 2005 R1.

  • Restart the main server.

  • If the main server has upgraded correctly, upgrade the standby to ClearSCADA 2007 R1.

  • Upgrade the ClearSCADA licence on the standby server.

  • Restart the standby server.

  • Configure the standby server to emulate ClearSCADA 2005 R1.

  • Restart the standby server.

  • Upgrade each client in turn to ClearSCADA 2007 R1.


Notes

  • It is important that the server that was the last to be shut down in a redundant pair is the first to be restarted to ensure that data received by this server is not overwritten by data from an older server.

  • Once the ClearSCADA 2005 R1 emulation has been enabled on both the main and standby servers, either ClearSCADA 2005 R1 or ClearSCADA 2007 R1 clients can be used to connect to the servers.

  • Once all of the clients have been upgraded to ClearSCADA 2007 R1, the ClearSCADA 2005 R1 emulation should be disabled on both the main and standby servers.

  • User favorites will not be accessible from non-ClearSCADA 2007 R1 clients.



ClearSCADA 2005 R0



ClearSCADA 2005 R0 Standalone Server


  • Shut the server down.

  • Upgrade the server to ClearSCADA 2007 R1.

  • Upgrade the ClearSCADA licence on the server.

  • Restart the server.


ClearSCADA 2005 R0 Main and Standby Servers with no Clients


  • Shut both the main and standby servers down.

  • Upgrade the main server to ClearSCADA 2007 R1.

  • Upgrade the ClearSCADA licence on the main server.

  • Restart the main server.

  • If the main server has upgraded correctly, upgrade the standby server to ClearSCADA 2007 R1.

  • Upgrade the ClearSCADA licence on the standby server.

  • Restart the standby server.


Notes

  • It is important that the server that was the last to be shut down in a redundant pair is the first to be restarted to ensure that data received by this server is not overwritten by data from an older server.


ClearSCADA 2005 R0 Main and Standby Servers with Clients


  • Shut both the main and standby servers down.

  • Upgrade the main server to ClearSCADA 2007 R1.

  • Upgrade the ClearSCADA licence on the main server.

  • Restart the main server.

  • Configure the main server to emulate ClearSCADA 2005 R0.

  • Restart the main server.

  • If the main server has upgraded correctly, upgrade the standby to ClearSCADA 2007 R1.

  • Upgrade the ClearSCADA licence on the standby server.

  • Restart the standby server.

  • Configure the standby server to emulate ClearSCADA 2005 R0.

  • Restart the standby server.

  • Upgrade each client in turn to ClearSCADA 2007 R1.


Notes

  • It is important that the server that was the last to be shut down in a redundant pair is the first to be restarted to ensure that data received by this server is not overwritten by data from an older server.

  • Once the ClearSCADA 2005 R0 emulation has been enabled on both the main and standby servers, either ClearSCADA 2005 R0 or ClearSCADA 2007 R1 clients can be used to connect to the servers.

  • Once all of the clients have been upgraded to ClearSCADA 2007 R1, the ClearSCADA 2005 R0 emulation should be disabled on both the main and standby servers.

  • User favorites will not be accessible from non-ClearSCADA 2007 R1 clients.




Go: Home Back

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of