Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

ClearSCADA 2007 R1 Changes To File Locations

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • ClearSCADA 2007 R1 Changes To File Locations
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 02:52 PM
0 Likes
0
764
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 02:52 PM

ClearSCADA 2007 R1 Changes To File Locations

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 09, 2021 11:52 PM

📖 Home  Back  
On a new installation of the latest ClearSCADA 2007 R1, the default directory structures have changed due to the support for Windows Vista and the new Microsoft requirements for file storage locations.

Please refer to the ClearSCADA online help for the most up to date information on installation defaults for your ClearSCADA version and operating system. The details below apply to ClearSCADA 2007 R1. While infrequent, these paths may change depending on operating system requirements and for this reason, please use the online help as the absolute guide for the installation paths.


When upgrading an existing system to ClearSCADA 2007 R1, existing file locations will be maintained. Only new Vista or Windows Server 2008 machines will enfore the file location rules.


For the database & log files, these are just the defaults, the actual locations are controlled by registry settings and configured on the location tab in the Server Configuration Tool.

The names of the database files have changed in this version, unless you are upgrading where the names will remain the same. For this reason, please ensure that the names of the files are correct for the machine they are being used on.


ClearSCADA 2007 Release 1 (Not Vista)



  File/Directory   Default Location
  ClearSCADA Database (Configuration)   C:\Documents & Settings\All Users\Application Data\ControlMicrosystems\ClearSCADA\Database\ClearSCADAConfig.dat
  ClearSCADA Database (Current Data)   C:\Documents & Settings\All Users\Application Data\ControlMicrosystems\ClearSCADA\Database\ClearSCADAData.dat
  Historic Data Directory   C:\Documents & Settings\All Users\Application Data\ControlMicrosystems\ClearSCADA\Database\History
  Event Journal Directory   C:\Documents & Settings\All Users\Application Data\ControlMicrosystems\ClearSCADA\Database\Journal
  Historic Files Directory   C:\Documents & Settings\All Users\Application Data\ControlMicrosystems\ClearSCADA\Database\HisFiles
  Data Files Directory   C:\Documents & Settings\All Users\Application Data\ControlMicrosystems\ClearSCADA\Database\DataFiles
  Log Files   C:\Documents & Settings\All Users\Application Data\ControlMicrosystems\ClearSCADA\Logs
  ViewX Alarm Sound Cache   C:\Documents & Settings\All Users\Application Data\ControlMicrosystems\ClearSCADA\ViewXAlarmSoundCache
  ViewX Cache   C:\Documents & Settings\All Users\Application Data\ControlMicrosystems\ClearSCADA\ViewXCache

Note that the name of the configuration file has been renamed from ClearSCADA.dat to ClearSCADAConfig.dat

The ViewX settings are now stored in the per-user application folder:
  File/Directory   Location
  ViewX Global Settings   C:\Documents & Settings\\Local Settings\Application Data\ControlMicrosystems\ClearSCADA\ViewX Global Settings.dat
  ViewX Head Settings   C:\Documents & Settings\\Local Settings\Application Data\ControlMicrosystems\ClearSCADA\ViewX Head Settings.dat


ClearSCADA 2007 Release 1 (Vista)



  File/Directory   Default Location
  ClearSCADA Database (Configuration)   C:\ProgramData\ControlMicrosystems\ClearSCADA\Database\ClearSCADAConfig.dat
  ClearSCADA Database (Current Data)   C:\ProgramData\ControlMicrosystems\ClearSCADA\Database\ClearSCADAData.dat
  Historic Data Directory   C:\ProgramData\ControlMicrosystems\ClearSCADA\Database\History
  Event Journal Directory   C:\ProgramData\ControlMicrosystems\ClearSCADA\Database\Journal
  Historic Files Directory   C:\ProgramData\ControlMicrosystems\ClearSCADA\Database\HisFiles
  Data Files Directory   C:\ProgramData\ControlMicrosystems\ClearSCADA\Database\DataFiles
  Log Files   C:\ProgramData\ControlMicrosystems\ClearSCADA\Logs
  ViewX Alarm Sound Cache   C:\ProgramData\ControlMicrosystems\ClearSCADA\ViewXAlarmSoundCache
  ViewX Cache   C:\ProgramData\ControlMicrosystems\ClearSCADA\ViewXCache

Note that the name of the configuration file has been renamed from ClearSCADA.dat to ClearSCADAConfig.dat

The ViewX settings are now stored in the per-user application folder:
  File/Directory   Location
  ViewX Global Settings   C:\Users\\AppData\Local\ControlMicrosystems\ClearSCADA\ViewX Global Settings.dat
  ViewX Head Settings   C:\Users\\AppData\Local\ControlMicrosystems\ClearSCADA\ViewX Head Settings.dat

Vista no longer uses the "Documents and Settings" directory used in earlier Windows versions for user and program data. These have been replaced by the "Users" folder and "ProgramData" folder.


ClearSCADA 2007 Release 0.1 or Older



  File/Directory   Default Location
  ClearSCADA Database (Configuration)   C:\ClearSCADADB\ClearSCADA.dat
  ClearSCADA Database (Current Data)   C:\ClearSCADADB\ClearSCADAData.dat
  Historic Data Directory   C:\ClearSCADADB\History
  Event Journal Directory   C:\ClearSCADADB\Journal
  Historic Files Directory   C:\ClearSCADADB\Files
  Log Files   C:\Program Files\Control Microsystems\ClearSCADA\Logs
  ViewX Alarm Sound Cache   C:\Documents & Settings\All Users\Application Data\Serck Controls\ViewXAlarmSoundCache
  ViewX Cache   C:\Documents & Settings\All Users\Application Data\Serck Controls\ViewXCache



Go: Home Back
  File/Directory   Default Location
  ViewX Global Settings   C:\Documents & Settings\All Users\Application Data\Serck Controls\ViewX Global Settings.dat

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore