ClearSCADA 2007 R0.2 Upgrade Strategy

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • ClearSCADA 2007 R0.2 Upgrade Strategy
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Application Programming 12
  • Setup 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Support 5
  • IoT 5
  • SCADA 5
  • Geo SCADA Expert 5
  • Drivers and Communications 4
  • Security 4
  • DNP 3 3
  • IEC 61131-3 Logic 3
  • Trends and Historian 2
  • Virtual ViewX 2
  • Geo Scada 1
  • ClearSCADA 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Architectures 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • OPC UA - Driver and Server
  • Requirements for Generating a Valid OPC UA Server Certificate
  • Load Events Using LoadRecord and LoadRecords
  • Geo SCADA Embedded Component Licenses
  • Geo SCADA 2023 Known Issues
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 10:38 AM
0 Likes
0
565
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 10:38 AM

ClearSCADA 2007 R0.2 Upgrade Strategy

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 09, 2021 07:38 PM

📖 Home  Back  


Upgrading from ClearSCADA 2005



A new feature has been added to ClearSCADA 2007 R0, that allows the ClearSCADA server to emulate previous versions (ClearSCADA 2005 R0 and R1). Please refer to the online help (Server Emulation Chapter of the Server Administration Guide) for further guidance on using this feature.

This is useful when upgrading systems with a large number of clients, as the format of mimics was changed between ClearSCADA 2005 and ClearSCADA 2007. The ClearSCADA 2007 ViewX client is capable of displaying mimics saved by both ClearSCADA 2005 and ClearSCADA 2007 ViewX clients. The ClearSCADA 2005 ViewX client can only display mimics saved by ClearSCADA 2005 ViewX clients. The server emulation feature allows ClearSCADA 2007 to appear as a ClearSCADA 2005 server, forcing ClearSCADA 2007 ViewX clients to save mimics in the ClearSCADA 2005 format. This then allows for a mix of ClearSCADA 2005 ViewX clients and ClearSCADA 2007 clients to be used with a ClearSCADA 2007 server.
NOTE: ClearSCADA 2007 requires a new license to be issued. ClearSCADA 2005 licenses will not validate against ClearSCADA 2007. Customers holding a valid support agreement with Control Microsystems are entitled to a license upgrade free of charge. To upgrade licenses please follow the procedure given in Updating Your ClearSCADA License


NOTE: After the upgrade, all user accounts with passwords that are longer than 16 characters will no longer allow the user to log on. The passwords on these accounts will need to be reset. User accounts with passwords that are 16 characters or less are not affected by this change.
 
When upgrading a system with separate clients and servers, the recommended strategy is to upgrade the clients before the servers. However this strategy was only adopted from ClearSCADA 2005 R1 and it is not possible to connect a ClearSCADA 2007 client to a ClearSCADA 2005 R0 server, because the ClearSCADA R0 server will reject connections from newer clients.  

The normal upgrade method for updating a main-standby system is to upgrade the standby server first, allow the two servers to synchronise, and then upgrade the main server.

NOTE: Because of changes to the main-standby functionality between ClearSCADA 2005 and ClearSCADA 2007, it is not possible to have a ClearSCADA 2005 standby server connected to a ClearSCADA 2007 main server.


Please follow the recommended Upgrade Process detailed below. 

ClearSCADA 2005 R0/R1 Standalone Server



  • Shut the server down.

  • Upgrade the server to ClearSCADA 2007 R0.2.

  • Upgrade the ClearSCADA license on the server.

  • Restart the server.


ClearSCADA 2005 R0/R1 Main and Standby Servers with no Clients



  • Shut both the main and standby servers down.

  • Upgrade the main server to ClearSCADA 2007 R0.2.

  • Upgrade the ClearSCADA license on the main server.

  • Restart the main server.

  • If the main server has upgraded correctly, upgrade the standby server to ClearSCADA 2007 R0.2.

  • Upgrade the ClearSCADA license on the standby server.

  • Restart the standby server.


NOTES:
  • It is important that the server that was the last to be shut down in a redundant pair is the first to be restarted to ensure that data received by this server is not overwritten by data from an older server.


ClearSCADA 2005 R0 Main and Standby Servers with Clients



  • Shut both the main and standby servers down.

  • Upgrade the main server to ClearSCADA 2007 R0.2.

  • Upgrade the ClearSCADA license on the main server.

  • Restart the main server.

  • Configure the main server to emulate ClearSCADA 2005 R0.

  • Restart the main server.

  • If the main server has upgraded correctly, upgrade the standby to ClearSCADA 2007 R0.2.

  • Upgrade the ClearSCADA license on the standby server.

  • Restart the standby server.

  • Configure the standby server to emulate ClearSCADA 2005 R0.

  • Restart the standby server.

  • Upgrade each client in turn to ClearSCADA 2007 R0.2.


NOTES:
  • It is important that the server that was the last to be shut down in a redundant pair is the first to be restarted to ensure that data received by this server is not overwritten by data from an older server.

  • Once the ClearSCADA 2005 R0 emulation has been enabled on both the main and standby servers, either ClearSCADA 2005 R0 or ClearSCADA 2007 R0 clients can be used to connect to the servers.

  • Once all of the clients have been upgraded to ClearSCADA 2007, the ClearSCADA 2005 R0 emulation should be disabled on both the main and standby servers.


ClearSCADA 2005 R1 Main and Standby Servers with Clients



If there are a small number of clients that can easily be upgraded:
  • Upgrade each client in turn to ClearSCADA 2007 R0.

  • Shut both the main and standby servers down.

  • Upgrade the main server to ClearSCADA 2007 R0.

  • Upgrade the ClearSCADA license on the main server.

  • Restart the main server.

  • If the main server has upgraded correctly, upgrade the standby server to ClearSCADA 2007 R0.

  • Upgrade the ClearSCADA license on the standby server.

  • Restart the standby server.


If there are a large number of clients or clients that cannot easily be upgraded (due to location, availability, etc.):
  • Shut both the main and standby servers down.

  • Upgrade the main server to ClearSCADA 2007 R0.

  • Upgrade the ClearSCADA license on the main server.

  • Restart the main server.

  • Configure the main server to emulate ClearSCADA 2005 R1.

  • Restart the main server.

  • If the main server has upgraded correctly, upgrade the standby to ClearSCADA 2007 R0.

  • Upgrade the ClearSCADA license on the standby server.

  • Restart the standby server.

  • Configure the standby server to emulate ClearSCADA 2005 R1.

  • Restart the standby server.

  • Upgrade each client in turn to ClearSCADA 2007 R0.


NOTES:
  • It is important that the server that was the last to be shut down in a redundant pair is the first to be restarted to ensure that data received by this server is not overwritten by data from an older server.

  • Once the ClearSCADA 2005 R1 emulation has been enabled on both the main and standby servers, either ClearSCADA 2005 R1 or ClearSCADA 2007 R0 clients can be used to connect to the servers.

  • Once all of the clients have been upgraded to ClearSCADA 2007, the ClearSCADA 2005 R1 emulation should be disabled on both the main and standby servers.




Upgrading from ClearSCADA 2007 R0 and later



When upgrading a system with separate clients and servers, the recommended strategy is to upgrade the clients before the servers.

The normal upgrade method for updating a main-standby system is to upgrade the standby server first, allow the two servers to synchronise, and then upgrade the main server.

Please follow the recommended Upgrade Process detailed below. 


ClearSCADA 2007 R0/R0.1/R0.11 Standalone Server



  • Shut the server down.

  • Upgrade the server to ClearSCADA 2007 R0.2.

  • Restart the server.


ClearSCADA 2007 R0/R0.1/R0.11 Main and Standby Servers with no Clients



  • Shut down the standby server.

  • Upgrade the standby server to ClearSCADA 2007 R0.2.

  • Restart the standby server and wait for it to fully synchronize to the main server.

  • Shut down the main server (the standby server will now takeover as the main server).

  • Upgrade the former main server to ClearSCADA 2007 R0.2.

  • Restart the former main server (this will synchronize to the new main server and become the standby server).


ClearSCADA 2007 R0/R0.1/R0.11 Main and Standby Servers with Clients



ClearSCADA 2007 R0/R0.1/R0.11 clients are fully compatible with a ClearSCADA 2007 R0.2 server. If you are not experiencing any of the issues with the ViewX client as resolved in the release notes, then there is no need to upgrade the ViewX clients.
  • Shut down and upgrade ViewX clients (if required).

  • Shut down the standby server.

  • Upgrade the standby server to ClearSCADA 2007 R0.2.

  • Restart the standby server and wait for it to fully synchronize to the main server.

  • Shut down the main server (the standby server will now takeover as the main server).

  • Upgrade the former main server to ClearSCADA 2007 R0.2.

  • Restart the former main server (this will synchronize to the new main server and become the standby server).


Support Assistance



For any problems with installing or upgrading ClearSCADA, please contact our Technical Support Department at mailto:technicalsupport@controlmicrosystems.com or through contact details shown here.

Go: Home Back

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now