Looking for anyone who has deployed Virtual ViewX Server for customers - host recommendations based on real-life experience?

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Looking for anyone who has deployed Virtual ViewX Server for customers - host recommendations based on real-life experience?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
318
AndrewScott
Admiral AndrewScott
109
BevanWeiss
Spock BevanWeiss
96
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
39
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Howard1
Ensign Howard1
Ensign

Posted: ‎2020-09-03 10:49 PM . Last Modified: ‎2023-05-03 12:11 AM

0 Likes
6
4276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-03 10:49 PM . Last Modified: ‎2023-05-03 12:11 AM

Looking for anyone who has deployed Virtual ViewX Server for customers - host recommendations based on real-life experience?

We're looking to deploy a Virtual ViewX solution for a customer to support 25 concurrent client connections.  The GeoSCADA installation doco recommends (for 20 clients) host with CPU passmark=15000, 2D Graphics passmark 300, 10 Cores, 32GB RAM, 1GB network.  I'm interested in whether anyone has any real life experience deploying a VVX server for this order of clients and can offer any insight or pit-falls to watch out for when spec'ing the server.  What have you used for the host - physical or virtual, if virtual with dedicated graphics resources, how successful was this in practice?  I'm really just wanting to draw on others experience to avoid known issues and propose best solution for the customer, as I haven'y personally deployed the VVX solution before...  Thanks! 

 

 

Labels
  • Labels:
  • Virtual ViewX
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AdamWoodland
AdamWoodland Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2020-09-07 10:50 PM

1 Like
5
4231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-07 10:50 PM

I haven't tried as high as 25, max so far is 10 using 8 cores/16GB of RAM. So far no complaints have made it my way, yet, but I'm not the active implementer or user of the system.

 

Some risk might be able to be managed by using a load balancer (e.g. cloud load balancer, web app firewall, or even just a small nginx on Linux) in-front of multiple servers to manage load. Haven't tried this so there may be some gotchas, but on paper it should/could work. It does use websockets so that might cause some problems as it did with OWASP rules in the WAF when I tried those.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-09-11 07:06 AM

In response to AdamWoodland
2 Likes
4
4204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-11 07:06 AM

Yesterday I saw 50 (yes, 50!) VVX web clients log in to an Azure F16v2 Server - 16 core CPU with SSD and 32Gb RAM.

Performance was tight, and complex mimics would stress the server a lot, but we had each client up with an alarm banner and new mimic changes up every 5 seconds. An F32 server with more cores would handle it better.

 

Note: to get this up and running with this number of clients, you must have a separate VVX server from Geo SCADA, and change the settings for sessions. Go to the VVX Manager applet. pick the Sessions tab. At the bottom choose "Multiple browser per session" and set a session count of 5. (All 50 users are still kept separate, but this allocates server resources to enable this sort of scalability).

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-09-14 05:39 PM

In response to sbeadle
0 Likes
2
4181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-14 05:39 PM

@sbeadle 

That is great to hear.

Was this with the default ViewX logging still enabled?

 

In some recent testing we've found the ViewX logging to be quite the bottle neck in general ViewX performance.

It would be great if you had the opportunity to disable logging on this server to just compare the performance.

 

The NVMe RAID SSDs that the F16v2 (and F32) use should obviously mitigate many of the disk 'media' read/write performance issues, but I'm running an NVMe SSD setup on my computer also, and just the disk subsystem impact (i.e. all the code executed to get a byte from the application to the disk) seemed to have a significant negative impact on performance. 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
AdamWoodland
AdamWoodland Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2020-09-07 10:50 PM

1 Like
5
4232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-07 10:50 PM

I haven't tried as high as 25, max so far is 10 using 8 cores/16GB of RAM. So far no complaints have made it my way, yet, but I'm not the active implementer or user of the system.

 

Some risk might be able to be managed by using a load balancer (e.g. cloud load balancer, web app firewall, or even just a small nginx on Linux) in-front of multiple servers to manage load. Haven't tried this so there may be some gotchas, but on paper it should/could work. It does use websockets so that might cause some problems as it did with OWASP rules in the WAF when I tried those.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-09-11 07:06 AM

In response to AdamWoodland
2 Likes
4
4205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-11 07:06 AM

Yesterday I saw 50 (yes, 50!) VVX web clients log in to an Azure F16v2 Server - 16 core CPU with SSD and 32Gb RAM.

Performance was tight, and complex mimics would stress the server a lot, but we had each client up with an alarm banner and new mimic changes up every 5 seconds. An F32 server with more cores would handle it better.

 

Note: to get this up and running with this number of clients, you must have a separate VVX server from Geo SCADA, and change the settings for sessions. Go to the VVX Manager applet. pick the Sessions tab. At the bottom choose "Multiple browser per session" and set a session count of 5. (All 50 users are still kept separate, but this allocates server resources to enable this sort of scalability).

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Howard1
Ensign Howard1
Ensign

Posted: ‎2020-09-13 11:22 PM

In response to sbeadle
0 Likes
0
4191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-13 11:22 PM

Thanks Steve - that is reassuring to hear!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-09-14 05:39 PM

In response to sbeadle
0 Likes
2
4182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-14 05:39 PM

@sbeadle 

That is great to hear.

Was this with the default ViewX logging still enabled?

 

In some recent testing we've found the ViewX logging to be quite the bottle neck in general ViewX performance.

It would be great if you had the opportunity to disable logging on this server to just compare the performance.

 

The NVMe RAID SSDs that the F16v2 (and F32) use should obviously mitigate many of the disk 'media' read/write performance issues, but I'm running an NVMe SSD setup on my computer also, and just the disk subsystem impact (i.e. all the code executed to get a byte from the application to the disk) seemed to have a significant negative impact on performance. 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-10-15 08:47 AM

In response to BevanWeiss
0 Likes
1
4001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-15 08:47 AM

ViewX logging was not enabled. However, there are changes proposed to logging to make it more granular and less noisy.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
  • SCADA integration
  • SCADA network
  • SCADA programming
  • SCADA software
  • scada system
  • SCADA tutorial
  • SCADA web application
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-10-19 03:36 PM

In response to sbeadle
0 Likes
0
3961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-19 03:36 PM

I see that GSE 2020 already includes some of the 'less noisy' works.  The cached registry read logging, which had been one of the huge performance impacts from my bench testing, is now suppressed.

 

Definitely looking forward to seeing more of the configurable logging with ViewX.

For the most part we don't have issues, so would prefer to be able to configure it to have very low overhead (i.e. disabled / minimal logging).

And we typically only report issues when they are reproducible, or at least recurring.  And in those situations we can enable logging for a period (and suffer the performance hit) to obtain detailed 'error' results.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.