Good day friends,
Im trying to receive modbus data from a power meter METSEPM5110 to controller P342020 which has serial modbus rj45 port. The meter has D1, D0, C and Shield terminals.
On the controller side (P342020) RJ45 port, I identified 4 and 5 pins are D1 and D0 respectively and pin 8 is Common. I connected accordingly using a terminal block.
Using the READ_VAR, I am not receiving data from meter.
baud rate is set to 9600, parity even
Link copied. Please paste this link to share this article on your social media post.
In Control Expert, did you setup the M340's serial port as a 2 wire RS485 modbus master running at 9600 baud with even parity? Did you change the default speed of the METSEPM5110 from 19200 to 9600?
If those are both setup then:
Link copied. Please paste this link to share this article on your social media post.
Solved brother. There was 1 offset in the modbus register. When I gave register number one less than in register in read var, data was read.
Thankyou