Using PAS600L as a transparent gateway between an M580 and Mitsubishi Q series

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Using PAS600L as a transparent gateway between an M580 and Mitsubishi Q series
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
106
Guillaume_Evrard
Captain Guillaume_Evrard Captain
51
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
32
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
Nel_77
Crewman Nel_77
Crewman

Posted: ‎2025-03-26 04:14 AM . Last Modified: ‎2025-03-26 04:16 AM

0 Likes
3
618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-26 04:14 AM

Using PAS600L as a transparent gateway between an M580 and Mitsubishi Q series

Hello experts,

Please I need some guidance.

I intend to use PAS600L as a transparent gateway for Modbus communication between two PLCs. A Schneider Electric M580 (on the Ethernet side) and a Mitsubishi Q series (on the RS-485 side). The panel server serial port (RS-485) will be configured in reverse mode as the Mitsubishi Q series connected at the serial port is required to act as a “client” by polling the M580.

I have the following questions:

  1. Is this set up workable?
  2. Which devices need a model on the PAS600L for proper communication—the M580, the Mitsubishi Q series, or both?
  3. If the M580 requires a model, does the PAS600L provide a native model for it as the M580 is a Schneider PLC, or must I create a custom model via EPC‑Web?

Thanks in advance for your help!

Labels
  • Labels:
  • Product selection
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-03-27 10:59 PM

1 Like
0
579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-27 10:59 PM

Hello @Nel_77 

Are you looking for a reverse modbus gateway ?

If yes this is doable by changing the configuration of the serial modbus port.

Guillaume_Evrard_0-1743141435640.png

 

You will have to configure the M580 as an unknown tcp device ( no model required) just to be able to assign a serial modbus id to your M580 example ID1= IP address of PLC:255.

Mitsubishi PLC will need to poll id 1.

You might have to change the timeout, but in your case default should be OK.

Pay attention that PAS will poll the M581 every 15s to check the connectivity, so not fully transparent.

Hope this answer your question,

Kind Regards

 

See Answer In Context

Reply
Replies 3
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-03-27 09:00 AM . Last Modified: ‎2025-03-27 09:02 AM

1 Like
0
597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-27 09:00 AM

Hello @Nel_77 , 


Panel Server cannot be a transparent gateway in Modbus Server mode (reverse mode).

 

According to the User Manual, Panel Server can be transparent gateway only for Modbus Serial devices (RS485 port) connected to a Modbus TCP master.

 

To allow your Mitsubishi PLC (Serial Master) to access to M580 (TCP Slaves), you will need to create a custom model for your M580 PLC (using the M580 summary table) with EPC-W tool. Upload this custom model inside your Panel Server and declare the M580 in Panel Server in your PAS600. Then => each M580 will have a unique Virtual ID.

 

Finally your Mitsubishi controller will access to the M580 through PAS600 IP address + each M580 Virtual ID attributed by PAS600.

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
Nel_77
Crewman Nel_77
Crewman

Posted: ‎2025-03-27 01:07 PM

0 Likes
0
573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-27 01:07 PM

Hello @Romain_Polette ,

Thank you so much for the clarification. Please how can I access this EPC web tool to create a custom model? 

 

Best regards,

Nel

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-03-27 10:59 PM

1 Like
0
580
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-27 10:59 PM

Hello @Nel_77 

Are you looking for a reverse modbus gateway ?

If yes this is doable by changing the configuration of the serial modbus port.

Guillaume_Evrard_0-1743141435640.png

 

You will have to configure the M580 as an unknown tcp device ( no model required) just to be able to assign a serial modbus id to your M580 example ID1= IP address of PLC:255.

Mitsubishi PLC will need to poll id 1.

You might have to change the timeout, but in your case default should be OK.

Pay attention that PAS will poll the M581 every 15s to check the connectivity, so not fully transparent.

Hope this answer your question,

Kind Regards

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of