Bonjour,
j'ai besoin de mettre à jour un PAS800L de V6 à V9 et j'ai un message d'erreur.
Que je passe par les pages Web embarquées ou par EPC, c'est la même chose.
Quelqu'un a déjà eut ce message?
"Update package signature verification failed"
"Signature invalide du groupement"
I need to update a PAS800L from V6 0 to V9 and I have an error message.
Whether I go through the embedded web pages or through EPC, it's the same thing.
Has anyone received this message before?
- Labels:
-
Legacy Gateways & Energy Servers
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Olivier_GARAULT
Can you please have a check on the PAS date and time settings. If it is not correct, please set the current date & time of your system and then proceed for update.
In this case i would suggest you to update the firmware by connecting one to one through webpage (direct, PAS to your laptop). If you still face the issue, please raise a support ticket with PAS logs.
Udhayakumar A K
ESXP System Support Expert
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Olivier_GARAULT
Can you please have a check on the PAS date and time settings. If it is not correct, please set the current date & time of your system and then proceed for update.
In this case i would suggest you to update the firmware by connecting one to one through webpage (direct, PAS to your laptop). If you still face the issue, please raise a support ticket with PAS logs.
Udhayakumar A K
ESXP System Support Expert
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Olivier_GARAULT ,
This is hapening when there is an issue with the bundle you try to install . As you tried using EPC and EWP this should not be the case. Have you tried to set date and time as highlighted by Udhayakumar ? Have you tried to install 1.8 just to try ?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thank's guys for your answers.
It's was the date. (1970)
Now the PAS800 is at the good date and good Firmware.