Hello @AAB_ALPS ,
You can directly wire the IFM to the RS485 port of the Panel Server.
We do not have Instruction Sheet giving some wiring details.
Ca va demander du bricolage... Old versions of the IFMs were easier to wire.
Please read the IFM IS to learn more about the pinout of the RJ45 (Modbus SL 2 wires):
You can also use the LV434211 as an adaptor:
Hi @Charles_Murison ! Can you move this topic to the Gateway section ? Thank.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
PAS is only having screw terminal not RJ45 for serial modbus and you need a small screwdriver.
If you have multiple RJ45 there is the splitter SE Tesys Lexium SD3 pretty convenient with wired terminals to the PAS or the Phoenix contact screw terminals to RJ45 adapter....
Link copied. Please paste this link to share this article on your social media post.
Hello @AAB_ALPS ,
I'm interested to have a feedback about your solution. How many IFM do you have connected to your Panel Server ?
@Guillaume_Evrard any experience with many IFMs connected to a PAS600/800 ?
One of our Panel Builder needs to connect up to 20 IFMs on the Panel Server (official recommendation is to limite 8x IFMs stacked to an IFE, but may apply to the PAS).
In theory, Panel Server can manage up to 32 Modbus serial devices. But IFM is not a pretty good device in term of communication performance. Customer will need to optimize the Modbus requests and use the IFM Dataset (need = read OF/SD status + Energy of Compact NSX).
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Hello @Romain_Polette,
I would say it depends on the speed of the serial modbus link + number of frames to be collected with number of registers and time it takes to return the RS485 bus by the IFM and if customer would like to collect data not to control. 20 using predefined model at 19200bps might be hard to achieve....
Link copied. Please paste this link to share this article on your social media post.
Hello @Romain_Polette,
Unfortunately we did not select the PAS600 solution with IFM, because it was not "good solution" for my client. We are staying with the IFE and IFM solution.
********************************************************************
Malheureusement nous n'avons pas sélectionner la solution PAS600 avec IFM, car cela n'était pas assez "propre" pour notre client. Nous somme rester avec la solution IFE et IFM.
Best regards
Link copied. Please paste this link to share this article on your social media post.
Hi,
Could you confirm if this could be done on LV434224 - Modbus SL HUB also ?
thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi all,
and Hi Guil,
I have a followup questions regarding the terminating resister. VW3A8306RC.
the setup is like this>
LV434002 - IFE Server stacked with 4x LV434224 - ModbusSL HUBS
this is the only photo i can gather: pic.jpg.
Question is do i need the VW3A8306RC Modbus line terminator resisters ? and if so how many? since only 1 ethernet cable is connected to the IFE Server ETH1 and nothing is occupying the IFM Hubs apart from the Modbus SL cord , does that mean i need 2x resisters connected per a IFM hub since there are 3 ports but 1 is connected to the NSX breaker via the cord..
Also the IFM Server have 2x empty ports.. does that require 2 additional VW3A8306RC ?
Link copied. Please paste this link to share this article on your social media post.
hello @wasabi
As per SL Hub documentation one modbus EOL is required at the end of the bus meaning the last SL hub opposite to the IFE....
Kind Regards