Re: Wiring PAS600L with NSX IFM

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Re: Wiring PAS600L with NSX IFM
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2022-11-23 05:01 AM . Last Modified: ‎2022-11-23 07:18 AM

2 Likes
9
3064
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-23 05:01 AM

Re: Wiring PAS600L with NSX IFM

Original thread here:

https://community.se.com/t5/EcoStruxure-Power-Monitoring/Wiring-PAS600L-with-NSX-IFM/td-p/415514

 

Hello @AAB_ALPS , 

You can directly wire the IFM to the RS485 port of the Panel Server.

We do not have Instruction Sheet giving some wiring details.

 

Ca va demander du bricolage... Old versions of the IFMs were easier to wire.

 

Please read the IFM IS to learn more about the pinout of the RJ45 (Modbus SL 2 wires):

https://download.schneider-electric.com/files?p_enDocType=Instruction+sheet&p_File_Name=NVE8539301-0...

 

You can also use the LV434211 as an adaptor:

Capture d’écran 2022-11-23 140340.jpg

 

Hi @Charles_Murison ! Can you move this topic to the Gateway section ? Thank.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Labels
  • Labels:
  • Commissioning
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
AAB_ALPS
Ensign AAB_ALPS
Ensign

Posted: ‎2022-11-23 06:14 AM

0 Likes
1
3052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-23 06:14 AM

Ok Merci, Thx.

 

On va bricoler :).

Tags (1)
  • Tags:
  • english
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2022-11-23 07:10 AM

0 Likes
0
3040
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-23 07:10 AM

PAS is only having screw terminal not RJ45 for serial modbus and you need a small screwdriver.

 

If you have multiple RJ45 there is the  splitter SE Tesys Lexium SD3 pretty convenient with wired terminals to the PAS or the Phoenix contact screw terminals to RJ45 adapter....

 

Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2023-04-04 08:02 AM

0 Likes
2
2671
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-04 08:02 AM

Hello @AAB_ALPS , 


I'm interested to have a feedback about your solution. How many IFM do you have connected to your Panel Server ?

@Guillaume_Evrard any experience with many IFMs connected to a PAS600/800 ?

 

One of our Panel Builder needs to connect up to 20 IFMs on the Panel Server (official recommendation is to limite 8x IFMs stacked to an IFE, but may apply to the PAS).

In theory, Panel Server can manage up to 32 Modbus serial devices. But IFM is not a pretty good device in term of communication performance. Customer will need to optimize the Modbus requests and use the IFM Dataset (need = read OF/SD status + Energy of Compact NSX).

 

Thanks.

Romain POLETTE
Solution Architect - France Operations
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-04-06 09:01 AM

0 Likes
0
2662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-06 09:01 AM

Hello @Romain_Polette,

I would say it depends on the speed of the serial modbus link + number of frames to be collected with number of registers and time it takes to return the RS485 bus by the IFM and if customer would like to collect data not to control. 20 using predefined model at 19200bps might be hard to achieve.... 

Reply
AAB_ALPS
Ensign AAB_ALPS
Ensign

Posted: ‎2023-04-07 01:57 AM

0 Likes
0
2657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-07 01:57 AM

Hello @Romain_Polette,

 

Unfortunately we did not select the PAS600 solution with IFM, because it was not "good solution" for my client. We are staying with the IFE and IFM solution.

********************************************************************

Malheureusement nous n'avons pas sélectionner la solution PAS600 avec IFM, car cela n'était pas assez "propre" pour notre client. Nous somme rester avec la solution IFE et IFM.

 

Best regards

Reply
wasabi
Lieutenant JG wasabi Lieutenant JG
Lieutenant JG

Posted: ‎2025-10-30 04:50 AM

0 Likes
1
400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-30 04:50 AM

Hi,

Could you confirm if this could be done on LV434224 - Modbus SL HUB also ?

 

thanks

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-11-02 10:49 PM

0 Likes
0
369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-02 10:49 PM

hello @wasabi ,

As it is RS485 modbus It should work.

Kind Regards

Reply
wasabi
Lieutenant JG wasabi Lieutenant JG
Lieutenant JG

Posted: ‎2025-12-09 11:22 PM . Last Modified: ‎2025-12-10 12:26 AM

0 Likes
1
46
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-09 11:22 PM

Hi all,

and Hi Guil,

I have a followup questions regarding the terminating resister. VW3A8306RC.
the setup is like this>

LV434002 - IFE Server stacked with 4x LV434224 - ModbusSL HUBS
this is the only photo i can gather: pic.jpg.

Question is do i need the VW3A8306RC Modbus line terminator resisters ? and if so how many? since only 1 ethernet cable is connected to the IFE Server ETH1 and nothing is occupying the IFM Hubs apart from the Modbus SL cord , does that mean i need 2x resisters connected per a IFM hub since there are 3 ports but 1 is connected to the NSX breaker via the cord..

Also the IFM Server have 2x empty ports.. does that require 2 additional VW3A8306RC ?

 

Attachments
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-12-09 11:59 PM

0 Likes
0
44
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-09 11:59 PM

hello @wasabi 

As per SL Hub documentation one modbus EOL is required at the end of the bus meaning the last SL hub opposite to the IFE....

Kind Regards

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore