Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Search in
Link copied. Please paste this link to share this article on your social media post.
Hello team,
From what i know, only 3 (/9) Power tag alarms, existing in the Panel Server WebPages, have been enabled within EEH : 80% rated current alarm, Communication loss alarm and Voltage loss alarm.
That means if we enable another alarm within the Panel Server (like Over voltage alarm or Zero current alarm) then this alarm won't do anything in EEH ?
Why didn't we activate all these alarms in EEH to avoid such a risk?
thanks for your clarification
Link copied. Please paste this link to share this article on your social media post.
Hello @PatrickPEREZ
The Panel server can publish to the cloud a maximum of 100 events/alarms (info from the user manual - § publication on SE cloud).
So if all the alarms are selected by EEH/ Energy Hub into the Panel Server, it will be possible to connect only 11 PowerTags and the selection of only 3 events/alarm per PowerTag offer the possibility to connect up to 33 for cloud publication.
BR
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.