PowerLogic and the Automation Server

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • PowerLogic and the Automation Server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
102
Guillaume_Evrard
Commander Guillaume_Evrard Commander
46
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
31
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
michael_franz
Admiral michael_franz
Admiral

Posted: ‎2016-06-15 09:06 AM

1 Like
6
1343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-15 09:06 AM

PowerLogic and the Automation Server

One place we have been able to jail break competitor's system is when they need PowerLogic meter data in a format that they can use.  This is often for alarming and HVAC demand load shed schemes.  An Automation server is a powerful way to read, log and display electrical data from Modbus meters and then feeding the values to another BMS through BACnet.  There are less expensive devices that do the simple translation if that is all the customer needs.  You can upsell the AS by showing it is an appliance that lives on their network and can provide good electrical data to them while allowing the resident BAS to get the data that they need.  Hospitals are a prime candidate for this kind of application due to the HIPAA consideration.

When properly engineered the Automation Server will live side by side with PME or other software systems needed to give the customer the required information.

Modbus from PowerLogic redirected out as BACnet Objects using an AS.  Kind-of-mostly getting this down.

Michael Franz

Technical Consultant

Faith Technologies

Tags (2)
  • Tags:
  • automation server
  • powerlogic
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa57752
sesa57752 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-06-15 12:18 PM

1 Like
1
1235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-15 12:18 PM

Hi Mike,

Nice post. The A/S is certainly a powerful device. I would also like to direct your attention to the StruxureWare™ Power Monitoring Expert and StruxureWare Building Operation Integration Design Guide and the Power Manager 1.2 for SmartStruxure™ Solution Design Guide for recommendations on which metering architectures to use. There are some compromises (lost functionality/performance) that should be considered when running PowerLogic meters through the A/S.

Regards---Mark

See Answer In Context

Reply
Replies 6
sesa57752
sesa57752 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-06-15 12:18 PM

1 Like
1
1236
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-15 12:18 PM

Hi Mike,

Nice post. The A/S is certainly a powerful device. I would also like to direct your attention to the StruxureWare™ Power Monitoring Expert and StruxureWare Building Operation Integration Design Guide and the Power Manager 1.2 for SmartStruxure™ Solution Design Guide for recommendations on which metering architectures to use. There are some compromises (lost functionality/performance) that should be considered when running PowerLogic meters through the A/S.

Regards---Mark

Reply
ram_kaushik
Admiral ram_kaushik Admiral
Admiral

Posted: ‎2016-06-15 03:16 PM

2 Likes
0
1235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-15 03:16 PM

Hi Mike,

Interesting point. There are always alternative architectures possible to integrate data from multiple systems - Mark brings up the SBO+Power Manager approach which is a great approach for non-critical facilities.

For critical facilities like hospitals which will benefit greatly from PME and applications like EPSS, I'd actually prefer to focus on up-selling PME-based critical power features and other application module functionality. To expose historical metering data to competitor BMS systems, one approach we've used is scheduling PME's "Data Export report" to dump out a csv file periodically. A competitor BMS uses a simple script to pick up these files and imports into their system. Doesn't address the real-time/alarming need but I'd contend that's better served from the PME end anyway.

Always many ways to skin a cat, eh?

Cheers!

R

Reply
michael_franz
Admiral michael_franz
Admiral

Posted: ‎2016-06-16 06:02 AM

1 Like
3
1235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-16 06:02 AM

Very familiar with PowerLogic software and hardware.  Cut my teeth on SMS over Blue Hose 25 years ago.  Can get SMS to sit up and speak.  Learning to do the same with PME.  Have played with Power Manager but not to much with ECO-Struxure for combining databases.  Several issues with the software offering.

1.  Has been complicated for customers to maintain - often goes fallow in time
2.  Can be difficult to get a PC on a sites network - IT people you know
3.  Engineers tool - complicated for the general user

The automation server is an appliance and I treat it as one.  We do not use its RS484 ports but instead run through gateways to gather the data.  This way when they are ready for Power Manager or PME it can be slid under the hood.  Another concern is that PME does not allow for segregated log in.  This makes it a tricky choice for an Enterprise level deployment.  Every site sees everyone's data and alarms.  Enterprise Server allow for the division of data for sites by log in credentials while allowing Enterprise data to be available for corporate users.  Why can't PME do this?

Michael Franz

Technical Advisor

Faith Technologies

Reply
sesa57752
sesa57752 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-06-24 11:10 AM

1 Like
2
1235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-24 11:10 AM

Hi Mike - Thanks for the summary! The log in credentials feature you mention is a known gap in PME. I'm not promising anything, but stay tuned for future versions! 😉

Reply
michael_franz
Admiral michael_franz
Admiral

Posted: ‎2016-06-24 12:22 PM

0 Likes
1
1235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-24 12:22 PM

Have been told that the Hierarchy Manager can help accomplish this or come close?  By making a Hierarchy structure can we create systems that segregate data and alarms?  Where do I learn how to do this if it can do the job?

Reply
sesa57752
sesa57752 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-06-28 02:57 PM . Last Modified: ‎2022-10-18 10:36 PM

2 Likes
0
1235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-28 02:57 PM

Hi Mike - Hmmm, not sure if Hierarchy Manager is the silver bullet for you.

Here is a link to a discussion on the HM & Alarms: https://community.se.com/message/87817#87817.

You can also search Exchange for Hierarchy Manager for the Hierarchy Manager Help Document & there are a couple of videos in the [PME] [Summary] Video Tutorials section of the Exchange.

Those can probably get you further along in understanding the Hierarchy Manager.

Regards--Mark

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of