Hi in latest release note for Panel Server with firmware 001.009.000 it is stated wireless device PowerTag Energy sensors 85
Is there any constraints regarding this number 85 if the energy sensor is 1-phase and/or 3-phase model ?.
Also the type of energy sensor connected (Paired) to the same Panel Server eg PowerTag F63, F160, PowerTag Rope, M250/630.
BR/Anders
Link copied. Please paste this link to share this article on your social media post.
Will try to elaborate in detail, please refer the below comments
1. Is there any constraints regarding this number 85 if the energy sensor is 1-phase and/or 3-phase model ?.
Ans:: Constraint is on Device type. For instance, if you use "PowerTag Energy sensors" type then you can connect 85 sensors with below any sensor model combination which is under same type.
Power meter |
PowerTag A9 M63 1P+N Bottom |
A9MEM1522 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 M63 3P |
A9MEM1540 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 M63 3P+N Top |
A9MEM1541 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 M63 3P+N Bottom |
A9MEM1542 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9MEM 1543 |
A9MEM1543 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag M250 3P 250A |
LV434020 |
001.003.002 |
001.003.002 * |
Power meter |
PowerTag M630 3P 630A |
LV434022 |
001.003.002 |
001.003.002 * |
Power meter |
PowerTag M250 3P+N 250A |
LV434021 |
001.003.002 |
001.003.002 * |
Power meter |
PowerTag M630 3P+N 630A |
LV434023 |
001.003.002 |
001.003.002 * |
Power meter |
PowerTag A9 M63 1P+W |
A9MEM1520 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 M63 1P+N Top |
A9MEM1521 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 P63 1P+N Top |
A9MEM1560 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 P63 1P+N Top |
A9MEM1561 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 P63 1P+N Bottom |
A9MEM1562 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 P63 1P+N Bottom RCBO |
A9MEM1563 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 F63 1P+N 110V |
A9MEM1564 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 F63 3P+N |
A9MEM1570 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 P63 3P+N Top |
A9MEM1571 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 P63 3P+N Bottom |
A9MEM1572 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 F63 3P |
A9MEM1573 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 F63 3P+N 110/230V |
A9MEM1574 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag F160 3P/3P+N |
A9MEM1580 |
001.003.002 |
001.001.000 * |
Power meter |
PowerTag Rope 200 A 3P/3P+N |
A9MEM1590 |
001.003.002 |
001.001.000 |
Power meter |
PowerTag Rope 600 A 3P/3P+N |
A9MEM1591 |
001.003.002 |
001.001.000 |
Power meter |
PowerTag Rope 1000 A 3P/3P+N |
A9MEM1592 |
001.003.002 |
001.001.000 |
Power meter |
PowerTag Rope 2000 A 3P/3P+N |
A9MEM1593 |
001.003.002 |
001.001.000 |
But incase if you are using the combination like "PowerTag M250 3P 250A" and "PowerLogic Tag Rope 120A 3P" then you cant exceed 40 because both are different device type ("PowerTag Energy sensors" and "PowerLogic Tag energy sensors").
2. Also the type of energy sensor connected (Paired) to the same Panel Server eg PowerTag F63, F160, PowerTag Rope, M250/630.
Ans:: Detailed in the Ans1.
Hope it helps!
Link copied. Please paste this link to share this article on your social media post.
Will try to elaborate in detail, please refer the below comments
1. Is there any constraints regarding this number 85 if the energy sensor is 1-phase and/or 3-phase model ?.
Ans:: Constraint is on Device type. For instance, if you use "PowerTag Energy sensors" type then you can connect 85 sensors with below any sensor model combination which is under same type.
Power meter |
PowerTag A9 M63 1P+N Bottom |
A9MEM1522 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 M63 3P |
A9MEM1540 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 M63 3P+N Top |
A9MEM1541 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 M63 3P+N Bottom |
A9MEM1542 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9MEM 1543 |
A9MEM1543 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag M250 3P 250A |
LV434020 |
001.003.002 |
001.003.002 * |
Power meter |
PowerTag M630 3P 630A |
LV434022 |
001.003.002 |
001.003.002 * |
Power meter |
PowerTag M250 3P+N 250A |
LV434021 |
001.003.002 |
001.003.002 * |
Power meter |
PowerTag M630 3P+N 630A |
LV434023 |
001.003.002 |
001.003.002 * |
Power meter |
PowerTag A9 M63 1P+W |
A9MEM1520 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 M63 1P+N Top |
A9MEM1521 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 P63 1P+N Top |
A9MEM1560 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 P63 1P+N Top |
A9MEM1561 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 P63 1P+N Bottom |
A9MEM1562 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 P63 1P+N Bottom RCBO |
A9MEM1563 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 F63 1P+N 110V |
A9MEM1564 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 F63 3P+N |
A9MEM1570 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 P63 3P+N Top |
A9MEM1571 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 P63 3P+N Bottom |
A9MEM1572 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 F63 3P |
A9MEM1573 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag A9 F63 3P+N 110/230V |
A9MEM1574 |
001.003.002 |
004.000.424 * |
Power meter |
PowerTag F160 3P/3P+N |
A9MEM1580 |
001.003.002 |
001.001.000 * |
Power meter |
PowerTag Rope 200 A 3P/3P+N |
A9MEM1590 |
001.003.002 |
001.001.000 |
Power meter |
PowerTag Rope 600 A 3P/3P+N |
A9MEM1591 |
001.003.002 |
001.001.000 |
Power meter |
PowerTag Rope 1000 A 3P/3P+N |
A9MEM1592 |
001.003.002 |
001.001.000 |
Power meter |
PowerTag Rope 2000 A 3P/3P+N |
A9MEM1593 |
001.003.002 |
001.001.000 |
But incase if you are using the combination like "PowerTag M250 3P 250A" and "PowerLogic Tag Rope 120A 3P" then you cant exceed 40 because both are different device type ("PowerTag Energy sensors" and "PowerLogic Tag energy sensors").
2. Also the type of energy sensor connected (Paired) to the same Panel Server eg PowerTag F63, F160, PowerTag Rope, M250/630.
Ans:: Detailed in the Ans1.
Hope it helps!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.