Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
29 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
why PAS800 Can not communicate with PM5350 Power meter ?
Link copied. Please paste this link to share this article on your social media post.
Hello,
It can communicate as soon as it is modbus. 2 options:
Kind Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
@Anonymous user We have had success by manually adding the device as a PM5110. It works as long as you do not try log or display measurements that are not supported by the PM5350.
For Example, if you try logging a harmonic that is not supported by the PM5350, the PM5350 will reply with an error.
This is not a nice solution, but it has work for the last few months for us.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.