PAS Firmware 1.7 - Changes to IO device name in published .CSV

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • PAS Firmware 1.7 - Changes to IO device name in published .CSV
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
98
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
43
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All
Related Products
product field
Schneider Electric
EcoStruxure Panel Server Universal
product field
Schneider Electric
EcoStruxure Panel Server Advanced

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Sam_Vosch
Lieutenant | EcoXpert Master Sam_Vosch Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-10-25 02:20 PM

0 Likes
4
897
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-25 02:20 PM

PAS Firmware 1.7 - Changes to IO device name in published .CSV

Hello,

After recently updating to firmware version 1.7 we noticed that the published .CSV file contents for IO devices changed. This completely broke our redundancy integration between the PAS devices and PME because the mapping in ETL no longer matches.

Old measurement name: IoCountMeasurement (L)
New measurement name: (L)

I could not find a mention of this change in the firmware 1.7.0 notes, but the issue is consistent across all our site that we updated to 1.7. 

  • Thumbnail of EcoStruxure Panel Server Advanced
    Schneider Electric
    EcoStruxure Panel Server Advanced
  • Thumbnail of EcoStruxure Panel Server Universal
    Schneider Electric
    EcoStruxure Panel Server Universal
View products (2)
Attachments
1_iod_WM7_20231025181312117.zip
Labels
  • Labels:
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: ‎2023-10-26 08:45 AM . Last Modified: ‎2023-10-26 08:49 AM

0 Likes
0
860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-26 08:45 AM

Hello Sam,
Can you confirm that, in Panel Server web pages, you have configured the IO in a pulse counter mode, I/O Contextualization set as "Custom" with "Consumption meter element name : empty and Consumption Unit set as "L"?

If yes and that you expect a Consumption element name in your export SFTP CSV file, set Consumption meter element name with for example IOCountMeasurement: if you expect IOCountMeasurement.
Regards
Eric

Eric_HAVAS_0-1698335134503.png

 

Reply
Sam_Vosch
Lieutenant | EcoXpert Master Sam_Vosch Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-10-26 03:22 PM . Last Modified: ‎2023-10-26 03:24 PM

0 Likes
0
840
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-26 03:22 PM

Hello,
Thank you for your reply. Sorry I should have given more context to the issue.
These are PAS800 (non L) devices connected to Smartlinks. These were working fine for a couple of months and provided logging of water meters. We were advised to upgrade to the latest firmware after all the issues we have been having with the older firmwares. Nothing else was changed in the PAS nor the Smartlink, just updated the PAS firmware.

 

We cannot change the measurements of the Smartlink in the PAS as the PAS downloads the names and types directly from the Smartlink device. We did not change anything in Smartlink configuration as they were working fine.


About a week after upgrading a few sites, we noticed there was no water data being processed by ETL. Digging into the files we can see that the new firmware for the PAS changed the measurement names. 

Thank you,

Sam_Vosch_0-1698358446868.png

 

Reply
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: ‎2023-10-26 11:07 PM . Last Modified: ‎2023-10-27 07:01 AM

0 Likes
0
824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-26 11:07 PM

Hello Sam,
Thanks a lot for your additional informations.
On this page, if you clic on the pen, you access directly at the end on this same PaS web page to the configuration of each Smartlink modbus channel: Have you applied my workaround on for example one channel?

Eric_HAVAS_0-1698386788648.png

 

I will be off for one week and not able to follow this topic, I encourage you, if it s not already the case,  to contact your local Customer Care Contact (which is the official technical support organization) with all info that will help them to deliver you an efficient support (Description of your architecture, autodiag and logs [mandatory] + your CSV files)

Reply
Sam_Vosch
Lieutenant | EcoXpert Master Sam_Vosch Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-10-29 02:59 PM

0 Likes
0
794
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-29 02:59 PM

Thank you for your continued support and clarification.

Unfortunately, no, I cannot apply your work around. There is no "Consumption Meter Unit Name field". Also, if I try change any values in the edit table, it will not save but give the error "Invalid object value" (See picture).

I already raised a support case, but I feel like the answer is, 'Yes this firmware changes the IO measurement naming, and you will need to either re-link the ETL maps or manually change the PAS IO naming (somehow)'.

Attachments
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of