Panel Server PAS600 replacement for COMX210

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Panel Server PAS600 replacement for COMX210
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
ArmandV
Lieutenant | EcoXpert Master ArmandV Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-01-10 04:37 AM

0 Likes
4
1949
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-10 04:37 AM

Panel Server PAS600 replacement for COMX210

Hi all,

 

The Panel Server PAS600 is recommended as a direct replacement of the COMX210 device.

It however looks like the panel servers are lacking valuable features of the COMX210 devices, such as the digital and analogue inputs.

Is there any other substitution device compatible with Power Monitoring Expert, which is also more comparable to the specs of the COMX210?

Regards,
Armand

Labels
  • Labels:
  • Product selection
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2023-01-10 04:40 AM

1 Like
3
1941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-10 04:40 AM

Hello @ArmandV , 

If you only need 2x DI => then use PAS600L commercial reference.

If you need more DI for pulse counting or breaker monitoring => then better use a Smartlink A9XMSB11.

Then all your Smartlink IO Channels will be compatible with PME. You will need to create Logical Device in Management Console.

 

Regards,  

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 4
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2023-01-10 04:40 AM

1 Like
3
1942
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-10 04:40 AM

Hello @ArmandV , 

If you only need 2x DI => then use PAS600L commercial reference.

If you need more DI for pulse counting or breaker monitoring => then better use a Smartlink A9XMSB11.

Then all your Smartlink IO Channels will be compatible with PME. You will need to create Logical Device in Management Console.

 

Regards,  

Romain POLETTE
Solution Architect - France Operations
Reply
ArmandV
Lieutenant | EcoXpert Master ArmandV Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-01-10 05:14 AM . Last Modified: ‎2023-01-10 05:15 AM

0 Likes
2
1932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-10 05:14 AM

Hi @Romain_Polette ,

Thank you for the feedback and advice.

Regards,
Armand 

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2023-01-10 06:00 AM

1 Like
1
1926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-10 06:00 AM

Hi @ArmandV , 

I forgot something important.

If you choose to use the 2x Digital Input embedded in a PAS600L, you will need to create a PME custom driver based on the Panel Server internal Modbus map. Because DI status / counting data are stored in the Panel Server. For the moment, no Panel Server driver is available for PME. 

If you choose the Smartlink Modbus, then it will be native to PME because the driver is native for many years.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
ArmandV
Lieutenant | EcoXpert Master ArmandV Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-01-10 06:04 AM

1 Like
0
1924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-10 06:04 AM

Thank you very much for the additional information on the PAS600L @Romain_Polette , that is good to know.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore