Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Panel Server (Ecostruxure) - Get live datas without Schneider Cloud

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Panel Server (Ecostruxure) - Get live datas without Schneider Cloud
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Romain_Polette Champion
125
Guillaume_Evrard
Guillaume_Evrard Leader
59
Randi_Dolan
Randi_Dolan Leader
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
EcoStruxure Panel Server

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
anbl_reel
anbl_reel
Explorer

Posted: ‎2023-05-03 01:04 AM . Last Modified: ‎2023-05-03 07:30 AM

0 Likes
8
4691
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-03 01:04 AM

Panel Server (Ecostruxure) - Get live datas without Schneider Cloud

Hello everyone !

 

Our client wants to avoid his data being sent to external clouds as much as possible (sensitive environment) such as Schneider Cloud. So, I made some researches on the Panel Server's user guide and I found that there were only two ways to publish datas which are export to Schneider Cloud or use SFTP (not very pratical to collect live datas). But I also saw on the web that it was possible to read datas only with the IP of the gateway if the gateway is connected to the internal network (wifi or ethernet) of the company through modbus tables and registers. My question is : can we get datas on real-time with this solution and after that to store and log these datas externally on a third-party supervision software.

 

Thank you in advance for your help 🙂

 
(I have seen you were informed on the subject @Guillaume_Evrard . Thank you a lot for your help and your time)
  • Thumbnail of EcoStruxure Panel Server
    Schneider Electric
    EcoStruxure Panel Server
View products (1)
Attachments
Labels
  • Labels:
  • Legacy Gateways & Energy Servers
Tags (5)
  • Tags:
  • cloud
  • ecostruxure
  • english
  • french
  • gateway
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
Guillaume_Evrard
Guillaume_Evrard Leader
Leader

Posted: ‎2023-05-03 09:19 PM

1 Like
5
4655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-03 09:19 PM

Hello,

Even with cloud connection to SE cloud it is not live data for measurements. The PAS is acting as a data logger, it is logging data on a periodic basis basis called sampling and pushing to the cloud at another periodic basis, as the COMX was doing.

There is except for alarm/event no difference between SFTP publication and cloud connection.

However PAS is also a modbus tcp gateway, so any monitoring system can poll the PAS to get the measurements from connected devices, as it is modbus you can get live data from the devices connected depênding on your master system (scada, BMS).

can you provide additional information ?

Reply
anbl_reel
anbl_reel
Explorer

Posted: ‎2023-05-04 12:37 AM . Last Modified: ‎2023-05-04 12:37 AM

0 Likes
4
4647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-04 12:37 AM

Image3.png

 

Hello,

There are two APIs (Schneider M340) in the network. Both of them will be linked with the panel server with MODBUS TCP (ethernet). We want to grab datas from the sensors, themselves connected in ethernet via MODBUS TCP to each APIs. These datas have to be on real time to know useful info such as functionning mode (manual, auto, ...). Do you need more additional information ? I don't really know what to give you more.

 

Thank you for you help @Guillaume_Evrard 

Attachments
Reply
Guillaume_Evrard
Guillaume_Evrard Leader
Leader

Posted: ‎2023-05-04 01:19 AM . Last Modified: ‎2023-05-04 01:20 AM

0 Likes
3
4643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-04 01:19 AM

Hello,

PAS 600 and PAS800 are having web pages to display measurements. PAS800 might get the same features as COMX510 (own web pages).

In your drawing can you explain what is your iot monitoring system ?

Would suggest to use a direct communication from a newer PLC directly to the cloud (As far as I remember M262 is having it)

Reply
anbl_reel
anbl_reel
Explorer

Posted: ‎2023-05-04 01:32 AM

0 Likes
2
4639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-04 01:32 AM

Thank you for the time you spend to help me @Guillaume_Evrard. The monitoring system is a website we give to ours client to allow them to monitor the system. It works by polling a database where the values of the datas we want to follow are stocked and logged (values of yesterday, today, ...). This database is fed thanks to the gateway (here the Panel Server) which collects and sends data from the MODBUS network to which it is connected (on the APIs diagram). The monitoring system is pretty much similar to EcoStruxure Power Monitoring Expert but we are especially interessed in dashboards (statistics).

Reply
Guillaume_Evrard
Guillaume_Evrard Leader
Leader

Posted: ‎2023-05-04 01:42 AM

0 Likes
1
4638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-04 01:42 AM

in that case SFTP publication and ETL to load your database with measurements from CSV ?

Reply
anbl_reel
anbl_reel
Explorer

Posted: ‎2023-05-04 02:07 AM

0 Likes
0
4636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-04 02:07 AM

ETL ?

The solution you are given to me concerns only datas at the end of the day or also the live datas ? I don't understand how we can have these live datas in the database with a CSV.

Reply
derickloo
derickloo
Explorer

Posted: ‎2023-10-12 09:34 PM

0 Likes
1
4018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-12 09:34 PM

Hi @anbl_reel , May I know you able to pull the data from the data logger without go through the built in web in the panel server?  Do they provide any API to do so?  

Reply
Szymon_Hochół
Szymon_Hochół Champion
Champion

Posted: ‎2023-10-18 07:25 AM

0 Likes
0
3995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-18 07:25 AM

Hi @derickloo ,

For the real-time data - you can retrieve the data over Modbus -> Examples of Modbus Routing - EcoStruxure Panel Server User Guide (schneider-electric.com)

For the historical data - you can retrieve the data via periodic CSV or JSON publication via SFTP -> Publication on SFTP Server - EcoStruxure Panel Server User Guide (schneider-electric.com)

 

BR

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore