Panel Server Advanced PAS800 RS-485 Modbus not connecting

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Panel Server Advanced PAS800 RS-485 Modbus not connecting
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
104
Guillaume_Evrard
Commander Guillaume_Evrard Commander
46
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
31
View All
Related Products
product field
Schneider Electric
EcoStruxure Panel Server Advanced

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
arl_renewables
arl_renewables
Cadet

Posted: ‎2025-07-08 08:38 AM

0 Likes
1
39
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-08 08:38 AM

Panel Server Advanced PAS800 RS-485 Modbus not connecting

I have had the pleasure of deploying a PAS800 for local data sampling and logging of a large panel board.

The actual switchgear is various Schneider types and the panel builder installed panel mounted power meters for the main incomer and all the outgoing ways.

The main incomer had a TCP/IP Modbus interface which I have had some success getting to work with a custom model imported to Panel Server. As with other users here, I failed to create a working model myself due to the "invalid" message, and so far have settled on a model for a similar meter which mostly works (some registers incorrect or missing)

 

I have turned my attention to the other power meters, which are all of the same type, and when the panel was built, linked together with a 2-wire RS-485 bus. This was connected to an older third-party data logger for which I have no access to the required software and I do not know if it was functioning properly or not.

 

I am trying to connect the RS-485 meters to the PAS800, and failing.

I did successfully create and import to the Panel Server a custom model file for it in EPC-W with the minimum set of required PDM registers.

I checked every meter and recorded its bus address. I checked the comms settings were the same on each, 9600, parity none, 1 stop bit. The settings in the Panel Server are the same.

Doing a detection took forever, so I aborted. I attempted to add a meter manually, and it first shows "connected" but immediately turns to "not connected" and stays that way.

 

One issue could the number of meters. There are 40+ meters, so over the 32 meter limitation. The bus length itself is limited as these are all in a single large LV panel. The RS-485 wiring appears to be a single daisy chain passed back and forth through DIN rail terminals. I am not sure if a termination resistor is present on the end remote from the Panel Server.

 

I attempted to connect a single meter, directly with a 2-wire bus. The communication likewise failed. However when asked to perform a discovery it did detect it as an unknown type.  The termination resistor was missing, could this alone cause complete bus failure?

 

Any pointers welcome. I am primarily an electrician with reasonable IT knowledge but no expert on these data systems.

 

From reading other posts I gather there can be problems with the number of devices and the timings/timeout periods, however I wasn't having any luck with a single meter either.

My understanding of the RS-485 port on the PAS800 is that D0/+ is RS-485+, D/0- is RS-485-, the next port for shielding and the 0V not used. 

  • Thumbnail of EcoStruxure Panel Server Advanced
    Schneider Electric
    EcoStruxure Panel Server Advanced
View products (1)
Labels
  • Labels:
  • Commissioning
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2025-07-09 09:24 PM

0 Likes
0
28
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-09 09:24 PM

hello @arl_renewables 

Starting with one meter is the right way to do.

What are your devices ?

For RS485 2Wires you need to have only +/- , sometimes +/6 are swapped from types of device.

If you are sure that the serial ports parameters are correct ( baudrate, parity, stop bit,...) this is perfect. PAS port should be terminated (line termination)  for modbus by selecting EOL yes in the config. Normally PAS should polarize the line. for a small bus run modbus EOL at the end of the bus is not required.

If you detect the device as unknown but keeps connected it is meaning that the Device is valid and register 0 is answering. reported as unknown because PAS is not able to find an embeded model to communicate with the Device.

In case of custom models the registers are used to check the communication, if the registers are wrong device might be reported as not connected even it is. You have to go to maintenance, communication and check the modbus statistics for exceptions. For RS485 exceptions displayed in the web pages are not exhaustive, you need to perform a diagnostic and check the diagnotic_modbus.txt file in the Zip that will be downloaded. Sometimes it is better to start with only one register and one frame and check the register before using a modbus tool.

PAS is also having a simple modbus tool to allow to check registers.

Kind regards

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login