Panel Server Advanced PAS800 RS-485 Modbus not connecting

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Panel Server Advanced PAS800 RS-485 Modbus not connecting
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
EcoStruxure Panel Server Advanced

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
arl_renewables
Crewman arl_renewables
Crewman

Posted: ‎2025-07-08 08:38 AM

0 Likes
3
697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-08 08:38 AM

Panel Server Advanced PAS800 RS-485 Modbus not connecting

I have had the pleasure of deploying a PAS800 for local data sampling and logging of a large panel board.

The actual switchgear is various Schneider types and the panel builder installed panel mounted power meters for the main incomer and all the outgoing ways.

The main incomer had a TCP/IP Modbus interface which I have had some success getting to work with a custom model imported to Panel Server. As with other users here, I failed to create a working model myself due to the "invalid" message, and so far have settled on a model for a similar meter which mostly works (some registers incorrect or missing)

 

I have turned my attention to the other power meters, which are all of the same type, and when the panel was built, linked together with a 2-wire RS-485 bus. This was connected to an older third-party data logger for which I have no access to the required software and I do not know if it was functioning properly or not.

 

I am trying to connect the RS-485 meters to the PAS800, and failing.

I did successfully create and import to the Panel Server a custom model file for it in EPC-W with the minimum set of required PDM registers.

I checked every meter and recorded its bus address. I checked the comms settings were the same on each, 9600, parity none, 1 stop bit. The settings in the Panel Server are the same.

Doing a detection took forever, so I aborted. I attempted to add a meter manually, and it first shows "connected" but immediately turns to "not connected" and stays that way.

 

One issue could the number of meters. There are 40+ meters, so over the 32 meter limitation. The bus length itself is limited as these are all in a single large LV panel. The RS-485 wiring appears to be a single daisy chain passed back and forth through DIN rail terminals. I am not sure if a termination resistor is present on the end remote from the Panel Server.

 

I attempted to connect a single meter, directly with a 2-wire bus. The communication likewise failed. However when asked to perform a discovery it did detect it as an unknown type.  The termination resistor was missing, could this alone cause complete bus failure?

 

Any pointers welcome. I am primarily an electrician with reasonable IT knowledge but no expert on these data systems.

 

From reading other posts I gather there can be problems with the number of devices and the timings/timeout periods, however I wasn't having any luck with a single meter either.

My understanding of the RS-485 port on the PAS800 is that D0/+ is RS-485+, D/0- is RS-485-, the next port for shielding and the 0V not used. 

  • Thumbnail of EcoStruxure Panel Server Advanced
    Schneider Electric
    EcoStruxure Panel Server Advanced
View products (1)
Labels
  • Labels:
  • Commissioning
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
arl_renewables
Crewman arl_renewables
Crewman

Posted: ‎2025-09-17 01:05 AM

2 Likes
0
470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-17 01:05 AM

To conclude this thread - I did reach a solution. I will briefly explain as it may benefit other users.

 

For the RS-485 bus, I physically proved the connection sequence of the bus throughout its length and added a termination resistor at the last device. At the PAS, I connected only the data pair. The earthed screen of the comms cable was connected to the frame of the enclosure.

For correct meter operation - this was due to my custom models being incorrect.

The Modbus documentation from the meter manufacturers proved to be inaccurate and inadequate.

 

A summary of what I needed to figure out to make my custom models work:

  • Using Function Code FC04 (not FC03) to read meter registers. Where not stated, the correct function code may be determiend by the modbus register address compared to the protocol norms.
  • Not using the entire register address as documented - this was incorrect and required "shortening"
  • Applying WORD_SWAP. Very annoying to work out - required research into MSB, LSB/big endian/little-big endian
  • Applying an address offset, if required
  • Using a computer and modbus software with USB to serial interface to scan registers to determine the correct addresses, offsets and data formats
  • Add all devices manually - my custom models lacked any identification information. Bus scans can take a huge amount of time and would have been fruitless. I was able to add dozens of meters manually relatively quickly.

 

All this requires a degree of trial and error with creating models in EPC-W and then verifying on the PAS. Start with a single parameter where you know what the value should be and go from there.

 

I also found in practice that more than 32 devices is working fine without a modbus repeater. The devices are within a single large panel so the total bus length is relatively short, probably less than 100 metres.

See Answer In Context

Reply
Replies 3
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-07-09 09:24 PM

0 Likes
1
686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-09 09:24 PM

hello @arl_renewables 

Starting with one meter is the right way to do.

What are your devices ?

For RS485 2Wires you need to have only +/- , sometimes +/6 are swapped from types of device.

If you are sure that the serial ports parameters are correct ( baudrate, parity, stop bit,...) this is perfect. PAS port should be terminated (line termination)  for modbus by selecting EOL yes in the config. Normally PAS should polarize the line. for a small bus run modbus EOL at the end of the bus is not required.

If you detect the device as unknown but keeps connected it is meaning that the Device is valid and register 0 is answering. reported as unknown because PAS is not able to find an embeded model to communicate with the Device.

In case of custom models the registers are used to check the communication, if the registers are wrong device might be reported as not connected even it is. You have to go to maintenance, communication and check the modbus statistics for exceptions. For RS485 exceptions displayed in the web pages are not exhaustive, you need to perform a diagnostic and check the diagnotic_modbus.txt file in the Zip that will be downloaded. Sometimes it is better to start with only one register and one frame and check the register before using a modbus tool.

PAS is also having a simple modbus tool to allow to check registers.

Kind regards

Reply
arl_renewables
Crewman arl_renewables
Crewman

Posted: ‎2025-08-04 04:49 AM

0 Likes
0
610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-04 04:49 AM

Thank you for your detailed reply.

 

The RS-485 devices are multiple units of the same meter type, Selec MFM384.

There a a few versions of this meter, I'm not sure exactly which flavour it is, however the modbus register tables look to be the same so that should not be an issue.

I had created and exported a custom model file from EPC Web and imported it to the PAS for this meter.

 

Thank you for the advise on checking the diagnostics, I will try this when returning to the site.

I will see if I can repeat my experiment with connecting to a single meter.

 

However if I can get one to work, I would still be subject to the 32 device limitation, without a repeater.

Is it the case that a repeater would be located anywhere in the bus prior to the 32nd device from the PAS?

Reply
arl_renewables
Crewman arl_renewables
Crewman

Posted: ‎2025-09-17 01:05 AM

2 Likes
0
471
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-17 01:05 AM

To conclude this thread - I did reach a solution. I will briefly explain as it may benefit other users.

 

For the RS-485 bus, I physically proved the connection sequence of the bus throughout its length and added a termination resistor at the last device. At the PAS, I connected only the data pair. The earthed screen of the comms cable was connected to the frame of the enclosure.

For correct meter operation - this was due to my custom models being incorrect.

The Modbus documentation from the meter manufacturers proved to be inaccurate and inadequate.

 

A summary of what I needed to figure out to make my custom models work:

  • Using Function Code FC04 (not FC03) to read meter registers. Where not stated, the correct function code may be determiend by the modbus register address compared to the protocol norms.
  • Not using the entire register address as documented - this was incorrect and required "shortening"
  • Applying WORD_SWAP. Very annoying to work out - required research into MSB, LSB/big endian/little-big endian
  • Applying an address offset, if required
  • Using a computer and modbus software with USB to serial interface to scan registers to determine the correct addresses, offsets and data formats
  • Add all devices manually - my custom models lacked any identification information. Bus scans can take a huge amount of time and would have been fruitless. I was able to add dozens of meters manually relatively quickly.

 

All this requires a degree of trial and error with creating models in EPC-W and then verifying on the PAS. Start with a single parameter where you know what the value should be and go from there.

 

I also found in practice that more than 32 devices is working fine without a modbus repeater. The devices are within a single large panel so the total bus length is relatively short, probably less than 100 metres.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore