Panel Server - 2 networks
Is it possible to configure ETH1 with a connection to a BMS network and ETH2 to a PMS network and provide both networks with the ability to read Modbus registers from the devices connected to the RS485 connection.
I've tried to implement it using the network examples in the guide but I can only read the Modbus data from ETH1 it isn’t working for ETH2 even though I can ping the IP assigned to ETH2.
Yes it is possible, I guess you are using seggregated networks with 2 networks on port 1 and port 2. By default the modbus gateway is enabled only on port 1, you have to enable it on port 2.