Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Search in
User | Count |
---|---|
108 | |
52 | |
46 | |
32 |
Link copied. Please paste this link to share this article on your social media post.
Is it possible to configure ETH1 with a connection to a BMS network and ETH2 to a PMS network and provide both networks with the ability to read Modbus registers from the devices connected to the RS485 connection.
I've tried to implement it using the network examples in the guide but I can only read the Modbus data from ETH1 it isn’t working for ETH2 even though I can ping the IP assigned to ETH2.
Modbus is enabled on both ETH1 and ETH2 ports.
Is there something I’m overlooking?
Link copied. Please paste this link to share this article on your social media post.
hello @Gavin_Bryson
Yes it is possible, I guess you are using seggregated networks with 2 networks on port 1 and port 2. By default the modbus gateway is enabled only on port 1, you have to enable it on port 2.
Kind Regards