We Value Your Feedback! Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services. Learn more about the survey or Click here to Launch the survey Schneider Electric Services Innovation Team!
Panel Server - 2 networks
Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2025-04-1709:30 AM
Panel Server - 2 networks
Is it possible to configure ETH1 with a connection to a BMS network and ETH2 to a PMS network and provide both networks with the ability to read Modbus registers from the devices connected to the RS485 connection.
I've tried to implement it using the network examples in the guide but I can only read the Modbus data from ETH1 it isn’t working for ETH2 even though I can ping the IP assigned to ETH2.
Yes it is possible, I guess you are using seggregated networks with 2 networks on port 1 and port 2. By default the modbus gateway is enabled only on port 1, you have to enable it on port 2.
Kind Regards
This is a heading
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.