Panel Server - 2 networks
Gateways and Energy Servers
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Panel Server - 2 networks
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
59
Randi_Dolan
46
Gavin_Bryson
Commander | EcoXpert Master Gavin_Bryson Commander | EcoXpert Master
Posted: ‎2025-04-17 09:30 AM
536
Is it possible to configure ETH1 with a connection to a BMS network and ETH2 to a PMS network and provide both networks with the ability to read Modbus registers from the devices connected to the RS485 connection.
I've tried to implement it using the network examples in the guide but I can only read the Modbus data from ETH1 it isn’t working for ETH2 even though I can ping the IP assigned to ETH2.
Modbus is enabled on both ETH1 and ETH2 ports.
Is there something I’m overlooking?
  • Product selection
Guillaume_Evrard
Captain
Posted: ‎2025-04-17 10:25 PM
hello @Gavin_Bryson
Yes it is possible, I guess you are using seggregated networks with 2 networks on port 1 and port 2. By default the modbus gateway is enabled only on port 1, you have to enable it on port 2.
Kind Regards