Hello,
we have a PM810 with a PM8M2222 on an EGX300MG.
Why we can see only 2 of the digital inputs on the EGX?
It is possible to create a driver with all necessary datas of the I/O card? (pulse count, calculated kWh and calculated kW in the PM8x0 device)
Thank a lot for your answer and have a nice day.
Link copied. Please paste this link to share this article on your social media post.
Hi Thomas,
The EGX300 has a tool where a custom device type can be made. More information about it is available here... https://powersolutionscommunity.schneider-electric.com/docs/DOC-1063
Using this tool, you can create a custom template to display whatever data is available onboard the PM800 Series Power Meter.
There are not currently any plans to revise the data displayed by the PM800 A-S1/A-S2 template.
Link copied. Please paste this link to share this article on your social media post.
Hi Thomas,
The EGX300 has a tool where a custom device type can be made. More information about it is available here... https://powersolutionscommunity.schneider-electric.com/docs/DOC-1063
Using this tool, you can create a custom template to display whatever data is available onboard the PM800 Series Power Meter.
There are not currently any plans to revise the data displayed by the PM800 A-S1/A-S2 template.