I want to log several parameter of my PM5350 using PAS800L, because of PM5350 did not detected on PAS800L, i got custom model addition and Import it form EPC - W, however after the template has successfully added, my PM5350 still did not detected by PAS800L, can anyone help me please. My PM5350 has been discover as ID = 1
Link copied. Please paste this link to share this article on your social media post.
Hello,
Are you using discovery to add your PM ? If yes you have to add your PM manually using the custom model you have loaded.
Discovery should detect an unknown device at slave ID 1 as you mention.
Kind Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Thank you so much for your help, it works, now I can Log PM5350 using PAS800L