PAS800 to HMIST6500 VIA MODBUS TCP

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • PAS800 to HMIST6500 VIA MODBUS TCP
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
96
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
41
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All
Related Products
product field
Schneider Electric
EcoStruxure Panel Server Advanced

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
MichaelFrancica1
Crewman MichaelFrancica1
Crewman

Posted: ‎2024-01-12 01:28 PM

1 Like
3
1323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-12 01:28 PM

PAS800 to HMIST6500 VIA MODBUS TCP

Hello,

Currently need to set up a simple demo for a client, the connectivity via Modbus TCP of an HMI model HMIST64500 and connected to one PAS800 panel server and downstream connected to a mixture of A9MEM1520 and A9MEM1590 to display on the HMI the various sensors parameters such as Amps, Volts, Active power, Hz and view trend logs together with basic PanelServer data such as connected devices , date/time, sensors health.  We are using the Ecostruxure Operator Terminal Expert to carry out HMI programming.

 

Appreciate to receive any assistance / guidance to create the basic terminal variables and to bind these with the screens as not yet successful in binding any of the registers and displaying on the HMI i.e. import the Modbus files for the various devices. according to DOCA0241EN-07.

 

Thankyou

 

  • Thumbnail of EcoStruxure Panel Server Advanced
    Schneider Electric
    EcoStruxure Panel Server Advanced
View products (1)
Labels
  • Labels:
  • PowerTag Energy
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2024-01-15 11:58 PM

0 Likes
2
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-15 11:58 PM

Hi @MichaelFrancica1 , 


We cannot help with the HMI programming but we can advice how to implement the Panel Server Modbus registers with any Modbus TCP client. 

 

First step:

check if the Modbus services are activated on the Panel Server:

Romain_Polette_0-1705391358363.png

 

Second step:

Write down all your PowerTag sensors Virtual ID.

You must send the Modbus request with Panel Server IP + device Virtual ID.

 

Third step:

Check if your HMI needs to be programmed with the Modbus register addresses (Hexadecimal in the DOCA0241EN) or with the Modbus registers numbers.

 

By following these steps, any Modbus client must be able to read the data of the devices connected to the Panel Server.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 3
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2024-01-15 11:58 PM

0 Likes
2
1311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-15 11:58 PM

Hi @MichaelFrancica1 , 


We cannot help with the HMI programming but we can advice how to implement the Panel Server Modbus registers with any Modbus TCP client. 

 

First step:

check if the Modbus services are activated on the Panel Server:

Romain_Polette_0-1705391358363.png

 

Second step:

Write down all your PowerTag sensors Virtual ID.

You must send the Modbus request with Panel Server IP + device Virtual ID.

 

Third step:

Check if your HMI needs to be programmed with the Modbus register addresses (Hexadecimal in the DOCA0241EN) or with the Modbus registers numbers.

 

By following these steps, any Modbus client must be able to read the data of the devices connected to the Panel Server.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
MichaelFrancica1
Crewman MichaelFrancica1
Crewman

Posted: ‎2024-01-25 02:05 PM

0 Likes
1
1242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-25 02:05 PM

Thankyou Romain for your reply.

 

We are following your suggestion, and confirm that the Modbus services are activated. We are using the Operator Terminal Expert with Modbus TCP Driver and IP address of the PAS800 (with IP address 169.254.157.128) and equipment address 255 and port 502. We need to read the Date and Time of the PAS800 with default ID: 255, and display on the HMI together with the phase to neutral voltage of one Power Tag M63 1P+W having virtual ID: 101. Hence for the date and time, we created var 1 - DATE and TIME and device address 400116. For the Power Tag, we created var 2 - REAL, 403028. We then created two numeric displays on the screen and assigned to both variables. When we simulate the program, the readings obtained are either 0, and with red border.

Can you kindly assist / guide ?

 

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2024-01-29 08:56 PM

0 Likes
0
1227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-29 08:56 PM

Hello @MichaelFrancica1 ,

Are you using switched port configuration ? Do you have modbus tcp server enabled on your PAS port ?

I would suggest to test first with a modbus tool (modscan, modpoll, etc...)

Pay attention to register and address . Address start at 0 whereas register start at 1

Voltage Metering Data 0x0BD3 3028 2 R - V Float32   0xFFC00000 N 3, 100-4 RMS phase-to-neutral voltage A-N

 

For voltage address in decimal is 3027, read holding register encoded in Float 32.

Can you try ?

Are you getting any exception code ?

Kind Regards

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of