PAS600L and IFM monitoring

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • PAS600L and IFM monitoring
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
99
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
44
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
BrianW
Lieutenant | EcoXpert Master BrianW Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-11-13 04:51 AM . Last Modified: ‎2023-11-13 05:57 AM

0 Likes
6
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-13 04:51 AM

PAS600L and IFM monitoring

Hi all,

I was wondering if anyone could assist with an issue I am having connecting a stack of four or five IFM devices to a Panel Server PAS600L. While the 600L sees the IFMs and shows they are in a connected state, but when I try to use the monitoring function to see what status the IFM is reporting from an NSX breaker (with a BSCM module and NSX cord SD cable), I am not seeing anything as seen in the attached screenshot. 

The firmware on the PAS600L is up to date. 

Also, IFM status works just fine using Modbus Poll through the PAS600L, so perhaps there is a setting that I have overlooked using the webpage?

 

Any suggestions would be wonderful...

regards,

Brian

Attachments
Labels
  • Labels:
  • Commissioning
  • Legacy Gateways & Energy Servers
Tags (3)
  • Tags:
  • english
  • ifm
  • PAS600L
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2023-11-13 09:26 PM

1 Like
0
1903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-13 09:26 PM

hello,

You are using serial modbus to the IFM ?

Have you tried to detect the devices using the PAS ? Normally you should detect the micrologic, not the IFM.

If detection does not work you can add the NSX manually bu selecting modbus ID and the model for your device. What we can see in your screenshot is a device without any datamodel (ie without any modbus table).

When using the embeded model PAS will detect the SN of the micrologic unit.

See Answer In Context

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2023-11-14 01:26 AM . Last Modified: ‎2023-11-14 01:30 AM

0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-14 01:26 AM

Hi @BrianW , 

 

What Modbus registers are you reading to have information from your IFMs ?


Please check that your NSX breakers have a communicating Micrologic and follow the procedure described by Guillaume.

Romain_Polette_0-1699954207913.png

 

If you do not have communicating Micrologic and need only information from the BSCM, you will need to create a Custom Model because BSCM is not a device native to the Panel Server.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 6
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2023-11-13 09:26 PM

1 Like
0
1904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-13 09:26 PM

hello,

You are using serial modbus to the IFM ?

Have you tried to detect the devices using the PAS ? Normally you should detect the micrologic, not the IFM.

If detection does not work you can add the NSX manually bu selecting modbus ID and the model for your device. What we can see in your screenshot is a device without any datamodel (ie without any modbus table).

When using the embeded model PAS will detect the SN of the micrologic unit.

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2023-11-14 01:26 AM . Last Modified: ‎2023-11-14 01:30 AM

0 Likes
0
1900
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-14 01:26 AM

Hi @BrianW , 

 

What Modbus registers are you reading to have information from your IFMs ?


Please check that your NSX breakers have a communicating Micrologic and follow the procedure described by Guillaume.

Romain_Polette_0-1699954207913.png

 

If you do not have communicating Micrologic and need only information from the BSCM, you will need to create a Custom Model because BSCM is not a device native to the Panel Server.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
BrianW
Lieutenant | EcoXpert Master BrianW Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-11-14 03:48 AM

1 Like
0
1892
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-14 03:48 AM

Thank you both, @Guillaume_Evrard & @Romain_Polette , this is very useful information to have. I'm just basically retrieving the breaker status from a BSCM & SD switch on the NSX cord via the IFM back to the PAS600L. As you mention Romain, I cannot detect the BSCM, which now makes sense if its not yet supported, so until I get some time, I am using the method suggested by Guillaume and manually selecting the MB address and model. This works very well. 

It would be nice and a bit faster in set up if the auto detection worked for BSCM, but for now, this is good!

Thank you both for your wisdom!! Also, I have noticed that, as seen with the digital inputs, that there seems to be a significant lag or delay until the software reports a change in status, sometimes up to 20~25 seconds. I have been informed that this is normal? 

Regards,

Brian

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2023-11-14 04:51 AM

0 Likes
1
1887
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-14 04:51 AM

Hi @BrianW , 

 

Regarding the DI status change delay, I suppose you are talking about the embedded Web services.

Can you check if you have the same delay when reading the DI status through Modbus TCP ?

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
BrianW
Lieutenant | EcoXpert Master BrianW Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-11-21 04:19 AM

0 Likes
0
1855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-21 04:19 AM

Hi @Romain_Polette 

 

I have just checked and see that the delay is down to about 6 or 7 seconds using Modbus TCP for changes in status from OPEN to CLOSED and vice versa. Using the Web service pages, this delay can be up to 20~25 seconds for each status change. 

 

I notice using the EPC, the status change is a lot quicker than the Web Service pages also, with delay times of about the same as Modbus TCP tests.

 

Hope this is of some help?

 

Regards,

Brian

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2023-11-22 12:18 AM

0 Likes
0
1837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-22 12:18 AM

Hi @Eric_HAVAS , 

Can you help us with the following questions ?

  1. Why delay on the PAS Web Page is about 20-25 sec when any change on the DI ?
  2. Is a delay of 7 sec expected when you check any DI status change through a Modbus TCP tool ?

Thanks.

Romain POLETTE
Solution Architect - France Operations
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of