PAS600L/PAS800L and WAGES
Bonjour,
Est-il possible de connecter ce type d'impulsion de compteur de gaz sur l'entrée numérique du PAS600L ou du PAS800L ? Les deux schémas électriques (relais Reed et détecteur inductif : voir fichier joint) sont-ils compatibles avec les caractéristiques techniques du PAS600L/PAS800L ?
Nota : J'ai noté que la largeur de l'impulsion doit être supérieure à 30 ms. Je vérifie cette caractéristique technique auprès du constructeur du compteur de gaz, mais merci de répondre à ma question.
Link copied. Please paste this link to share this article on your social media post.
2023-02-2702:31 AM
Hello,
If you refer to Universal Panel Server instruction sheet (UPas IS ), pulse counter compliant to IEC62053-31 are supported by Panel Server . So I advise In first to check with ELSTER if their Gaz counter is conform to this standard to garanty full compatibilty (simpler that an individual analyze of each characteritic)