Hi All,
We are facing issue while integrating 3rd party meters to PME through PAS600.
Even in modscan it is not giving data continuously(with in 10polls it is dropping 1 or 2 times), where as through RS485 to USB converter data coming continuously.
Custom file uploaded and Timeout changed to 1000ms,but issue is same.
Please provide a solution, if any one faced issue and resolved.
Link copied. Please paste this link to share this article on your social media post.
Hi @SureshYadavT ,
We were facing a similar issue with 3rd party devices. When connecting up to 14 or 15 devices, the polling went very smoothly and without any problems. But when more devices were connected, the polling suddenly became very slow and finally didn't work anymore. We also tried to play with the settings but without any success. In our case to provide a quick solution to the customer, we decided to split the bus into 2 lines with 2 seperate PAS, also when it is not ideal case.
Link copied. Please paste this link to share this article on your social media post.
hello @SureshYadavT ,
Can you provide details on the configuration of the devices in the PAS, are they configured in the PAS, if yes using a model or unknown device or you are using transparent gateway (nothing) ? How many devices do you have ? any modbus statistics available ?
Any issue on the serial line ( polarization, termination, etc...)
Can you provide the modbus diag ?
Kind Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
hello @SureshYadavT,
Have you configured the devices in PAS or not ? (please show the PAS device page). Need to understand if you are using transparent gateway or not.
Can you show the the modbus stats (in communication ) or send the diagnostic_modbus.txt file from the full log ?
are you using switched port config ? If yes do you have modbus server enabled on ETH (normally yes) ?
Not sure to understand, when you poll 20 registers it is working from modcsan and PAS EWP, but for 10 registers I do not see if you get answer from the EWP ?
Might be easier for you to contact Technical Support.
Kind Regards
Link copied. Please paste this link to share this article on your social media post.
Hi @SureshYadavT,
"Custom file uploaded and Timeout changed to 1000ms,but issue is same."
Could be interesting to know what are the errors :
I understand you have multiple 3rd party devices connected to your PAS600 (device ID = 4, 5, 66, 89).
=> How many devices in your serial line ? Only 4 ?
=> Are these device IDs from the devices themselves ? Or Virtual IDs attributed by PAS600 when you declare a device on its Web interface ?
=> All the same device model / manufacturer ?
Modscan is connected to your PAS600 IP and you are addressing each devices as following:
Supposing ID 66 and 89 are the same ref of device:
Supposing ID 4 and 5 are the same ref of device:
What you can try during your Modscan testing with each device:
Regards,