Hello.
Good afternoon.
Has anyone here ever succeeded in reading data from the PAS600L in Json format in real time using sftp mode?
My SFTP server is correct and normal json with a duration of 10 minutes is saved. but I need json that can read data in real time to manage error reporting.
Link copied. Please paste this link to share this article on your social media post.
Hi,
From my experience with the PaS, for real time-data use Modbus (TCP) to poll the PaS (for the digital inputs) or communicate directly with the meters attached to the PaS (PaS acting as a passthrough gateway and not a data logger) using something like PME, EBO, SCADA, etc.
I'm not sure if the PaS team implemented the ability to directly poll the PaS for any zigbee/wireless connected devices, if not, the old solution was to have a 2nd PaS in a parent-child configuration and then the parent PaS can be polled via modbus for the downstream zigbee devices on the child PaS. There's more info on the architectures in the PaS user guide.
Data export is not real-time, the fastest it can publish logged data is every 10mins. In addition, the json data file needs mapping from the ID's to human-readable names (there's an enhancement request logged for the PaS to export the topology with the json data file to allow the mapping to be automated). The CSV export uses the human-readable names in the data file.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Hello @bedjojaya ,
Real time data for downstream devices are only available through Modbus TCP (or Modbus Serial if you set Panel Server in Server Mode).
There is no embedded API to allow real time data access through HTTPS.
SFTP is clearly not adapted for real time data viewing.
Regards,