Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
29 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
Can you please confirm if PAS600 Panel server can collect data into Modbus serial line devices through a Link 150 gateway ?
Best
GE
Link copied. Please paste this link to share this article on your social media post.
Hello @Gingko_Elec ,
This will be possible soon.
Just waiting the developers to deliver the version 001.003.001.
@Dom-Socquet Do you have visibility when the next PAS600 release will be available on se.com ?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Hello Gingko Elec,
Yes, it is possible.
In this architecture, the Link 150 will be designed as a “child gateway” for the Panel Server.
For this architecture, PAS600 firmware must be Version 001.003.001 or higher.
Link copied. Please paste this link to share this article on your social media post.
Hello @Gingko_Elec ,
This will be possible soon.
Just waiting the developers to deliver the version 001.003.001.
@Dom-Socquet Do you have visibility when the next PAS600 release will be available on se.com ?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.