Hi,
have a PAS800 connected to a RMH (LV481004)
The RMH has no function for easy termination of line resistor (120ohm).
The question is if it is realy nessecary? Could it be included in the RMH already?
It works without fine without, but generally it should be a line resistor in all topology`s star/ serial.
BR
GIA
Link copied. Please paste this link to share this article on your social media post.
Hello @geir_eas_no_bfo ,
You can consider the following general rules for RS485 2 wires bus:
Panel Server integrate both polarization and termination features.
If you have only an RMH connected to the Panel Server, its fine to remove termination on both side of the bus (deactivate feature on PAS).
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @geir_eas_no_bfo ,
You can consider the following general rules for RS485 2 wires bus:
Panel Server integrate both polarization and termination features.
If you have only an RMH connected to the Panel Server, its fine to remove termination on both side of the bus (deactivate feature on PAS).
Regards,
Link copied. Please paste this link to share this article on your social media post.