Logging capacity (number of days) ComX510

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Logging capacity (number of days) ComX510
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
YvesR
Ensign YvesR Ensign
Ensign

Posted: ‎2016-03-16 07:42 AM

1 Like
12
3414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-16 07:42 AM

Logging capacity (number of days) ComX510

Hello,

I'm trying to find some info about the logging capacity of the ComX510

I know if I got 1 device with 2 quantitys to log it's gonna take some serveral years to have a full memory

But is there some calculation to do to know exact how many dyas are left?

And what happens if the memory is full is this a FIFO?

We had this on the egx300 but can find it on the comX510

thankx

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Michael_Khela
Ensign Michael_Khela Ensign
Ensign

Posted: ‎2016-03-21 12:22 PM

2 Likes
9
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-21 12:22 PM

Hi Yves,

The Com'X510  can store 30 topics logging every 5 min for two years before it runs out of memory and start FIFO the data

Hope that helps you with your calculation

Best Regards

See Answer In Context

Reply
Replies 12
Michael_Khela
Ensign Michael_Khela Ensign
Ensign

Posted: ‎2016-03-21 12:22 PM

2 Likes
9
3131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-21 12:22 PM

Hi Yves,

The Com'X510  can store 30 topics logging every 5 min for two years before it runs out of memory and start FIFO the data

Hope that helps you with your calculation

Best Regards

Reply
Jun_Escano
Lieutenant JG Jun_Escano Lieutenant JG
Lieutenant JG

Posted: ‎2016-05-23 07:30 AM

0 Likes
7
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-05-23 07:30 AM

Hello Michael,

Is there something like a calculating tool for this? I have seen the formula:

32 Devices * 30 topics * 4 samples/hour (15 min interval) * 24 hours a day * 365 days per year * 2 year = 67.276.800 which guarantees 2 year historical data.

But what are topics? is one topic a parameter called for example kWh? Or is each parameter defined as the selected parameter in the list (kWh total, kWh phase 1, kWh phase 3) . For a BCPM 84 point it will mean that if you want to log the kWh you could either have one topic or 84 topics.

Unfortunately we have a customer who is working with a COMX510 with 9 x BCPMA084S where he wants to log kWh and kVA....

=> 9 devices * 168 topics * 4 samples / hour * 24 hrs a day * 365 days per year * 2 year = 105.960.960 ==> how many years?

Hope you can help

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2016-05-26 11:42 AM

1 Like
6
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-05-26 11:42 AM

Hi Jun.

For maximum performance, we would not recommend any more than 2 BCPM's per Com'X.  In simple terms...this is due b/c the Com'X treats each of the BCPM connected circuits as a device.

The amount of storage is equal to...32 devices, 30 topics each at 15 minute intervals = 25 months of data. 

The Com'X cannot store more than 25 months of data....this is static.  After 25 months, the data will FIFO.


James

Reply
Yu_Diao
Commander Yu_Diao Commander
Commander

Posted: ‎2016-05-26 08:30 PM . Last Modified: ‎2023-02-06 01:15 AM

0 Likes
1
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-05-26 08:30 PM

James,

 

Admittedly, I have never even gotten close to the max logging cap, but I have been tracking this topic for a while. From what I found here https://community.exchange.se.com/t5/Gateways-and-Energy-Servers/Com-X510-Standalone-Logging-Time/td... , it indicates that ComX 510 max logging space is around 2G, and it also mentioned that "The calculation above can be adapted...adding more devices, and less topics plus longer intervals or some variation"

 

So, does the "25 months of data" is a software/firmware enforced cap, which no matter how little topics/devices are logged in ComX 510, it just simply cannot exceed 25 months logged data or should we continue to conduct the calculations considering the actual device number/topic/logging interval and the 2G max logging space?

 

Regards,

Reply
Jun_Escano
Lieutenant JG Jun_Escano Lieutenant JG
Lieutenant JG

Posted: ‎2016-05-27 12:59 AM

0 Likes
3
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-05-27 12:59 AM

Hi James,

I know that you have recalled the max 2 bcpm during the webex. Unfortunately we were blind in the topology of the customer site but they mentioned that they normally used the egx300 and used it in various locations.  Luckily the interval they asked is just 1 time per day which means that a maximum performance could not be that critical. Eventually they want to check / export data every month. 

I hope that there will be a good tool in future whichtakes exceptional products such as the BCPM into account so we could determine the max logging capacity of the COMX510

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2016-05-31 06:59 AM

0 Likes
2
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-05-31 06:59 AM

Thanks Jun.  I will add your comments to my list.

James

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2016-05-31 07:03 AM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-05-31 07:03 AM

Correct...25 months is a static time-frame.  We may allow in the future a firmware change to increase the time period, but for now it is static.

James

Robert Jennings

Bobbie Meredith

Reply
KuanKhoon
Lt. Commander KuanKhoon Lt. Commander
Lt. Commander

Posted: ‎2016-06-27 12:58 AM . Last Modified: ‎2023-02-06 01:12 AM

0 Likes
1
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-27 12:58 AM

Hi James,

 

I did raise the question of the logging capacity (we calculated to be 201,830,400 entries) of the ComX 510 and the prospect of upgrading the SD card (which we found that the unit only uses 2GB of space) back on 16th Jan 2016. The thread is Com'X510 Standalone Logging Time

 

Does the above 25 month limit supersede your previous insight into the devices where you stated in https://community.se.com/message/79855#79855

 

"The Com'X 510 can support 32 devices at 30 topics each at 5 minute intervals for 2 years of stored historical data. 

The calculation above can be adapted...adding more devices, and less topics plus longer intervals or some variation."

 

That means that my conclusion later on in https://community.se.com/message/80270#80270

is not correct,

 

" If I were to do the following maths, (32 devices) x (30 topics) x (12 entries per hour) = 2 years

We derive a total of (32devices x 30topics/device x 12entries/hour x 24hour/day x 365day/year x 2years) = 201,830,400 entries (wow! 200 million entries ++)

 

Using the above base number, we should be able to freely determine the total logging time according to number of devices, topics, logging entries per hour, etc. Is this calculation reasonable?"

 

 

Best Regards,

 

Tan Kuan Khoon

Senior Specialist, PAE

Schneider Electric Singapore

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2016-06-27 12:33 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-27 12:33 PM

Robert Jennings - Can you comment for KK?

James

Reply
Anonymous user
Not applicable

Posted: ‎2016-12-24 10:36 PM

2 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-12-24 10:36 PM

Hi, can I have the official documentation of COMX510 data looging capacity stating those calculation? My client requested this official document to be submitted.

We have configured comx510 at 5min logging interval (with 5 to 20 devices connected in each Comx510, each device having 15 topics) and he want to keep at least 3months data before FIFO.

rolly

Reply
Bernhard_Huener
Ensign Bernhard_Huener Ensign
Ensign

Posted: ‎2017-11-13 08:56 AM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-11-13 08:56 AM

Hello Team Com'X,

we are seeking answers to the above raised questions as well.

Where do we stand?

Thanks

Bernhard

Reply
KuanKhoon
Lt. Commander KuanKhoon Lt. Commander
Lt. Commander

Posted: ‎2018-01-17 06:17 PM

0 Likes
0
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-01-17 06:17 PM

Hello Everyone,

I can confirm after running the ComX 510 for over 2 years the following is true,

1) Logging limit of 2 year, first in first out. Does not matter how many variables you are logging

2) The number of variables logged and at what frequency determine how much memory will be consumed

    - 4GB of SD will almost certainly never be consumed

    - 40 topics at 1 minute logging for 2 years consumed 0.9GB (my unit is still saying it has 3.1GB free)

3) There is another thread that says the ComX 510 can only link up to 64 devices (32 on local RS-485 and another 32 via external Link150 aggregation). If that is confirmed, then we can safely say that the unit will never fill up and the full log retention period is 2 years, regardless of topics/max 64 devices/logging intervals.

Best Regards,

KK

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore