Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
29 | |
28 |
Posted: 2015-12-14 05:17 AM
Link copied. Please paste this link to share this article on your social media post.
Hi,
As per my knowledge serves, it is possible to view all Devices connected to EGX 100/300 connected on same LAN with Com'X 510 to be viewed on ComX web pages. as shown in Image below.
Is it possible to configure same way for two Com'X 510, to view data of all the devices connected to both Com'X 510 via a single Com'x web page ( single IP address) image attached.
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Hello Mufish,
Yes, you can set this up in the Com'X 510. Just be sure to enable the Modbus gateway on the Com'X connected to the serial devices.
Alternatively...you could use the Link150 as a gateway to the serial devices connected to the one Com'X 510.
Thanks,
James
Link copied. Please paste this link to share this article on your social media post.
Hi Mufish,
Just moved this to the Gateways and Energy Servers area. James Jeanette, would you be able to direct this question?
Posted: 2015-12-15 12:23 AM
Link copied. Please paste this link to share this article on your social media post.
Thanks...
I had changed the tag.
Link copied. Please paste this link to share this article on your social media post.
Hello Mufish,
Yes, you can set this up in the Com'X 510. Just be sure to enable the Modbus gateway on the Com'X connected to the serial devices.
Alternatively...you could use the Link150 as a gateway to the serial devices connected to the one Com'X 510.
Thanks,
James
Posted: 2015-12-15 08:53 PM
Link copied. Please paste this link to share this article on your social media post.
Thanks
James Jeanette.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.