I need to read the communication or TCP/IP port status of EQX100 over SNMP, can anyone help me to know the Object ID for this parameter?
Thanks
Md Aamir Rahmani
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello Waqas,
Thanks for your Reply!!
I didn't find any document attached. Can you please load the document.
BR
Md Aamir Rahmani
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
EGX100 has the standard MIB2 inside.
It never had the Transparent Factory (Schneider's Private MIB) inside.
There is no need to download any MIB file, a simple MIB Browser software (Network Management / Network Monitoring / SNMP Monitoring / MIB Browser ) can return you the full OIDs tree, if you enable the SNMP setting in EGX100.
The private Schneider MIB is for other Schneider devices:
Of interest may be this OID subtree: .1.3.6.1.2.1.6.13