How to use Mastepact model with IFE

Gateways and Energy Servers

Get expert answers to your questions regarding Schneider Electric Gateways & Energy Servers, from product selection to implementation and troubleshooting. Collaborate with a global community of experts and peers, get support and share your experiences by subscribing to the Schneider Electric Community Gateways and Energy Servers forum today.

sesa41698_bridg
Lt. Commander Lt. Commander
Lt. Commander

How to use Mastepact model with IFE

The "Masterpact" models provided by the Com'X 200/210 are designed for a direct connexion :

            Micrologic <->  BCM (modbus) <-> Serial line

With some modification it is possible to use those models for Masterpact connected through an IFE  :

            Micrologic <->  BCM (ULP) <-> IFE <-> Ethernet port

Attachments
8 Replies 8
sesa57006_bridg
Crewman Crewman
Crewman

Re: How to use Mastepact model with IFE

Can you confirm this instruction is only a temporary work around until IFE full support? Availability date of full support?

sesa41698_bridg
Lt. Commander Lt. Commander
Lt. Commander

Re: How to use Mastepact model with IFE

Yes this is a temporary solution.

We were not able to include the Masterpact Micrologic interfaced by the IFE, as there is a discrepancy between the document and the product (in the user manual powers are expressed in kW, while in the product the powers are expressed in 100 W).

Recently IFE has decided to modify the user manual,

We will create a native model it in a future version


     Regards

MagnusEngstrom
Ensign Ensign
Ensign
0 Likes
0
359

Re: How to use Mastepact model with IFE

How about the Com'X 510?

In the document, it is stated that it is applicable only for 200/210.

JamesJeanette
Commander Commander
Commander
0 Likes
0
359

Re: How to use Mastepact model with IFE

Hi Magnus!

At the top, there is a reference to Com'X 510.

7193

- Can you please confirm.

James

sesa41698_bridg
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
359

Re: How to use Mastepact model with IFE

Since version 1.1.43, the Com'X 510 automatically recognise the Masterpact / IFE.

NOTE : in order to discover It, you must launch a modbus discovery between slave 255 and slave 255

(In IFE, the ULP devices is mapped as modbus slave 255);

7196

7197

Regards

Jef

sesa41698_bridg
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
359

Re: How to use Mastepact model with IFE

Sorry the details of the document preview is not very clear.

If we download the doc we obtain this :

7198

Which is correct : This note does not apply to the Com'X 510 !

MagnusEngstrom
Ensign Ensign
Ensign
0 Likes
0
359

Re: How to use Mastepact model with IFE

I am asking because yesterday I upgraded the firmware of a Com'X 510 to version 1.1.44 in our showroom.

It only detects an unknown device at address 255 ...

Btw: The Com'X 510 is the one James sent me a few weeks before the fair beginning of May.

Could there be an issue with this one? Pre-series build or something? I will check it's "About" for the f/w version to see if it was properly loaded (via USB-stick in the front). Can't do that until next week though ...

sesa41698_bridg
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
358

Re: How to use Mastepact model with IFE

I have tested it with a version 1.1.43 and an IFE LV434011 version 001.009.008.

I know that some IFE have got wrong Firmware image with a wrong modbus identifier code.

Could you use "Modbus tester" and FC 43-14 to check that the 43-14 code is corrcect :

7194

If you do not have ModbusTester, I can send it to you

     Regards

     Jef