How to get Modbus register of the Wireless Temperature Sensor (TH110 and CL1010) from comX?

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • How to get Modbus register of the Wireless Temperature Sensor (TH110 and CL1010) from comX?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
96
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
41
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
mykel
Lieutenant JG mykel
Lieutenant JG

Posted: ‎2020-10-08 10:22 PM

0 Likes
8
4085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-08 10:22 PM

How to get Modbus register of the Wireless Temperature Sensor (TH110 and CL1010) from comX?

Hi Good day everyone,

 

Kindly advice on how to get the correct Modbus registers for the wireless temperature devices (TH110 & CL110). Please see the attached PDF file for the system architecture.

 

 

Also here is the screen shot of ZBRN32_registers_Ting v0.2 which is from our partner but we are not familiar how to use it:

 

in this image i use 55 as Input no. referring for the device Channel Number.

ZBRN32_registers_Ting v0.2_Screenshot.PNG

 

And using the Com'X Diagnostic>> Read Device Register>>

I am expecting to read the same reading from the sensor to confirm that it is the right register.

ComX Diagnostic.PNG

 

 

 

 

 

 

reading from device.

temp: 31.4

Humidity: 69.14

comx-device reading.PNG

 

 

 

 

 

Kindly advice.

Thank you in advance.

Attachments
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2020-10-09 01:55 AM

0 Likes
1
4071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-09 01:55 AM

Hello @mykel , 

 

To see the detailed frame, you need to go under  :

  1. Custom Library tab
  2. Select your Model Name
  3. Under the "Slave" section click on "Edit Frame" button 

You will see the detail of all consecutive frames associated to the main "Frame" you set for your custom mode.

 

Regards.

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 8
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2020-10-09 12:11 AM . Last Modified: ‎2020-10-09 12:16 AM

0 Likes
3
4077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-09 12:11 AM

Hello @mykel , 


I have tested with CL110 connected to Channel 1 of my ZBRN32 and it works well.

 

Below the frame I used in my custom model to monitor Temp and Humidity for Channel 1.

ComX_CL110_CH1_model.png

 

Values confirmed on my Com'X interface.

ComX_CL110_CH1_values.png

 

To read the correct registers it seems you need to read the Holding Register and not the Register Address set into your Custom Model.

Example below : To read temperature I set Register Address to 16 in my Custom Model. But to read the value in the Diagnostic tab you need to put the Holding Register = Register Address + 1 = 17

ComX_CL110_CH1_readregisters.png

 

I think there is a gap in your Partner document : 1829 = Register Address for Battery Voltage. So to read this value you need to put 1830 in "Starting Register" and read 1 register.

 

 

Regards.

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
mykel
Lieutenant JG mykel
Lieutenant JG

Posted: ‎2020-10-09 01:29 AM

0 Likes
2
4073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-09 01:29 AM

Hi @Romain_Polette ,

 

Thank you for fast response.

 

I wonder if it is possible for me to view the setting for "Digital Frame Item Description" of the device that is already configured?

Maybe i can use this to get the register that was used for the devices.

 

Thank you.

Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2020-10-09 01:55 AM

0 Likes
1
4072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-09 01:55 AM

Hello @mykel , 

 

To see the detailed frame, you need to go under  :

  1. Custom Library tab
  2. Select your Model Name
  3. Under the "Slave" section click on "Edit Frame" button 

You will see the detail of all consecutive frames associated to the main "Frame" you set for your custom mode.

 

Regards.

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
mykel
Lieutenant JG mykel
Lieutenant JG

Posted: ‎2020-10-21 01:19 AM

1 Like
0
4056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-21 01:19 AM

Good day,

 

Yesterday i was able to visit the site and confirm that this way works for me.

 

Thank you.

Tags (1)
  • Tags:
  • english
Reply
YonKhoerul
Ensign YonKhoerul Ensign
Ensign

Posted: ‎2023-08-24 07:38 PM

0 Likes
0
3183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-24 07:38 PM

Hello, Teams,

Where can I get a list of addresses to read channels on ZBRN32,

I have an issue where I can't read the thermal on the ZBRN connected to the TM251 PLC,

To read the access I connect directly to the PLCTM251 and read the ID listed for ZBRN32 or the PLC ID.?

for one ZBRN installed a total of 59 sensors.

we use two ZBRN with the same total sensor.

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2023-08-24 10:29 PM . Last Modified: ‎2023-08-24 10:30 PM

1 Like
0
3176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-24 10:29 PM

Hello,

It depends on the configuration of your ZBRN, can you confirm if it is ZBRN1, ZBRN2 or ZBRN32 ?

You have 2 modes of operation.

  • One ID, all the measurements are available on one modbus id and you have to increment the register address by +33 to access sensors.
  • One ID per sensor, there is one modbus id per sensor and you are always getting the mesurement at the same adress.

for one ID : 

Register number Register Number Register Address Register Number Register Address Sologate input
RSSI (8bits) Time out (8 bits) Temperature (16 bits) Temperature (16 bits) RH (16 bits) RH (16 bits)  
Value in dBm
'-128 = undefined
- 0x00 : Ok
- 0xFF : Timeout expired
0,01°C 0,01°C 0,01% 0,01%  
12 17 16 18 17 0
45 50 49 51 50 1
78 83 82 84 83 2
111 116 115 117 116 3
144 149 148 150 149 4
177 182 181 183 182 5

If you are using ZBRN32 you have to get the timeout in order to validate the measurement, as it will provide always the last measurement received. 

ZBRN1/2 are providing NaN in timeout conditions

Reply
charlesvds
charlesvds
Cadet

Posted: ‎2024-03-07 11:28 PM

0 Likes
1
2282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-03-07 11:28 PM

Hello Team,
I am looking for the Modbus address map for the ZBRN32. It seems to be slightly different from the ZBRN1 and 2 which is causing me some headaches. There does not appear to be a ZBRN32 equivalent document to the Harmony Hub ZBRN1/ZBRN2 User Manual.
The ZBRN32 also has an additional option when configuring the serial port parameters. It just displays a t . 0
I presume this is a timeout. Does anybody have more information on this ?
Thank you in advance.

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2024-03-10 10:17 PM

0 Likes
0
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-03-10 10:17 PM

Hello,

Normally ZBRN2 and ZBRN32 menu are identical.

If you want to get data from TH110/CL110 same register except that for ZBRN32 you have to validate the measurement based on timeout information. For ZBRN1/2 you get NA in case of timeout condition.

If you refer to T in this menu :

  ConF Configuration menu (Conf)  
  in.nn Show the quantity of binding devices nn = [0-60]
  SL Serial Link setting menu  
  T  s Table Selection Allow selection of table selection to use one UID per E-Access or one UID per device (multi UID feature)
  T  s Table Selection Value s = [0 - 4]
0: One UID per E-Access
1-4: One UID per sensor

 

This is Table selection. If you have 0 all sensors are at the same modbus adress but sensors are distributed over several modbus registers (+ 33).

If you put 1, 2, 3, 4. Each sensor will be a different modbus address and registers will always be the same per sensor.
Number defines the starting address for the first sensor.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of